Do you know if whether V*A gives a close approximation to watts, or whether the power factor is large enough (or small enough) to make that inaccurate?
Do you know if whether V*A gives a close approximation to watts, or whether the power factor is large enough (or small enough) to make that inaccurate?
Mark,
Thank you for the response. The chart is very helpful.
Matt
V*A is certainly an upper limit because it assumes a PF of 1 but over a pump's head curve, the motor load can vary from around 40% to 100% and the power factor is dependent on load. At peak load the PF is usually not better than 0.9 but I haven't measured it directly on a pump. The following paper shows some of the effects but in general, I don't think you can count on the PF being close to 1 for an induction motor. There is always a reactive part to the power.
http://www1.eere.energy.gov/manufact...s/10097517.pdf
The best way to measure pump power is by using the power company meter on the side of the house. You can get a measurement with the pump vs off and get a much better estimate as long as nothing else changes in the house between measurements. I have a digital meter and it is pretty easy to get the power difference but you can do the same with the old style analog meters too.
Mark
Hydraulics 101; Pump Ed 101; Pump/Pool Spreadsheets; Pump Run Time Study; DIY Acid Dosing; DIY Cover Roller
18'x36' 20k plaster, MaxFlo SP2303VSP, Aqualogic PS8 SWCG, 420 sq-ft Cartridge, Solar, 6 jet spa, 1 HP jet pump, 400k BTU NG Heater