Thread: choosing a timer for pump on new construction inground pool

  1. #1
    Join Date
    May 2014
    Location
    Midatlantic USA
    Posts
    2

    Default choosing a timer for pump on new construction inground pool

    Hi everyone. Just registered today for the forum since my inground Grecian vinyl liner pool is almost finished. I was asking the electrician about timers for the pump, and he said to ask my pool builder. But then the pool builder said to ask the electrician. So what can anyone tell me about a timer? The pool is built but the electrician has not been out to do the hookups and switches yet. What do I want to ask for? And how should it be installed? Thanks!

  2. #2
    CarlD's Avatar
    CarlD is offline SuperMod Emeritus Vortex Adjuster CarlD 4 stars CarlD 4 stars CarlD 4 stars CarlD 4 stars CarlD 4 stars CarlD 4 stars
    Join Date
    Dec 1969
    Location
    North Central NJ
    Posts
    6,607

    Default Re: timer for pump on new construction inground pool

    The timer is almost certainly a 220v one, and should either be installed in your basement, near your breaker panel (pump should have a ground-fault breaker) or in a protected out-building like a shed. Many jurisdictions (like mine) REQUIRE a timer to meet code. Mine was installed by the electrician who did all the pump wiring.
    Carl

  3. #3
    Join Date
    May 2014
    Location
    Midatlantic USA
    Posts
    2

    Default Re: timer for pump on new construction inground pool

    Quote Originally Posted by CarlD View Post
    The timer is almost certainly a 220v one, and should either be installed in your basement, near your breaker panel (pump should have a ground-fault breaker) or in a protected out-building like a shed. Many jurisdictions (like mine) REQUIRE a timer to meet code. Mine was installed by the electrician who did all the pump wiring.
    Thanks, Carl, for the reply. I think maybe the electrician and I weren't communicating. So I'll go back to him (after I research this a little more). I had no idea some areas require a timer. How long do you run yours? I've been reading about recent studies saying 4 hours a day is enough, but that seems scary. Also, when you shock, do you need to override the timer to make it run?
    Last edited by neefer; 05-02-2014 at 10:20 PM.

  4. #4
    CarlD's Avatar
    CarlD is offline SuperMod Emeritus Vortex Adjuster CarlD 4 stars CarlD 4 stars CarlD 4 stars CarlD 4 stars CarlD 4 stars CarlD 4 stars
    Join Date
    Dec 1969
    Location
    North Central NJ
    Posts
    6,607

    Default Re: timer for pump on new construction inground pool

    Oh, now THAT is a COMPLETELY different question!

    Lots of factors come into it. I have solar panels so my motivation is to run it MORE when the sun shines, especially like...now...when the water's cold.

    Rule of thumb is to "turn over the water each day" but that is actually probably more than you need, maybe even double what you need as long as you're properly chlorinating.

    Notice I didn't give you a direct answer....because each pool and situation is different.
    Carl

  5. #5
    PoolDoc's Avatar
    PoolDoc is offline Administrator Quark Inspector PoolDoc 5 stars PoolDoc 5 stars PoolDoc 5 stars PoolDoc 5 stars PoolDoc 5 stars PoolDoc 5 stars PoolDoc 5 stars
    Join Date
    Jan 2005
    Location
    Georgia
    Posts
    11,386

    Default Re: timer for pump on new construction inground pool

    . . . . membership updated.

    A couple of points:

    1. Your timer needs are determined by the pump motor specs: voltage, amps, run time, pump speeds.

    2. If you have 2 pumps (pool and vacuum, etc.), you may want a SINGLE integrated timer. With 2 timers, if they get out of sync, the vac pump can be turned on when the pool pump is off . . . damaging the vac pump.

    3. Electromechanical timers are more reliable than electronic timers, which can die during thunderstorms.

    4. Outdoor timers need outdoor cases . . . which cost extra. Alternatively, build a tiny 'shed' roof over your timer board.

    5. It's possible to turn a 240V pump off using a SPST (one switch) timer, but doing so leaves 120V present on one of the power leads, creating a shock hazard for unsuspecting service people (or homeowners). Use a DPST (one switch for each power line) on 240V pumps.

    6. Example timers at Amazon:
    24hr 120v timer (SPST)
    24hr 240v timer (DPST) in a plastic outdoor case
    24hr 240v timer (DPST) in a metal indoor case
    2 Timers, arranged to provide Hi/Lo/Off control of a 2-speed pump

+ Reply to Thread

Similar Threads

  1. Timer for Pool Cover Pump
    By nelsongg in forum Pool Startup, Shutdown, & Winter Operation
    Replies: 0
    Last Post: 02-15-2013, 07:05 AM
  2. Timer for pool pump - any recommendations ?
    By Rsam5 in forum --cleanup--
    Replies: 2
    Last Post: 10-09-2012, 10:38 PM
  3. Choosing a pool pump
    By Carolina in forum Pool Equipment & Operations
    Replies: 2
    Last Post: 08-26-2012, 09:18 AM
  4. Choosing a new pump/filter for my pool
    By ryankenn in forum Pool Equipment & Operations
    Replies: 10
    Last Post: 06-22-2012, 10:18 PM
  5. Question about heat pump pool heater and fireman's switch on pump timer
    By HuntnHog in forum In-Ground Pool Construction and Repair
    Replies: 1
    Last Post: 04-20-2011, 07:37 PM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts