    Quote Originally Posted by PoolDoc View Post
    Offering electrical advice over the Internet always makes me really nervous, but . . . you seem to understand what you are looking and how to use a meter, so here goes.

    The fireman's switch circuit you ID'd on the Starite can be connected to any control device or safety, so long as ALL devices are connected in series, not in parallel. In series connections, if any switch fails, the circuit is open (infinite ohms). The circuit is 'connected' or enabled only when ALL switches are closed (> 0.3 ohm)

    In millivolt heaters, it is absolutely critical that this circuit must be 'clean' and low resistance, since such heaters operate on tiny voltages and amounts of current. On electronic, transformer driven, heaters such as yours, this is not quite so critical, but still good practice.

    It appears that the Jandy has a controlled SP-NO (single pole, normally open) relay in the heater position. This circuit is NOT powered by the Jandy (no voltage), but makes or opens any 24v circuit connected through it. It is NOT to be used with line voltage (>100v) but only with control voltages (<26v).

    That said, it appears you can simply unplug the short yellow "fuse" jumper, cut it, and splice it using insulated butt splice connectors.
    .

    The heater cannot shut on without the filter pump running. If the pump shuts off so does the heater. Install guy said that was the way it needed to be and I cannot find anything suggesting otherwise.

    The wiring should take no more than 15 minutes. I'll let you know how it went.

    Thanks PoolDoc

  2. #2
    PoolDoc's Avatar
    PoolDoc is offline Administrator Quark Inspector PoolDoc 5 stars PoolDoc 5 stars PoolDoc 5 stars PoolDoc 5 stars PoolDoc 5 stars PoolDoc 5 stars PoolDoc 5 stars
    Join Date
    Jan 2005
    Location
    Georgia
    Posts
    11,386

    Default Re: Pool heater connection issue

    Hm-mh. I overlooked something important. Timers are not commonly used on pools in much of the Southeast, and I forget things that I haven't often had to deal with.

    Anyhow, heater's have thermal safety's that SHOULD shut the heater off, if the pump is off. But it's not good to depend on that.

    If your Jandy unit does not automatically turn off the pump BEFORE turning the heater off, you'll need to put a flow switch in series with the Jandy control unit, so if flow is low, the heater cannot fire.

  3. #3
    Join Date
    May 2013
    Location
    Newcastle, CA
    Posts
    5

    Default Re: Pool heater connection issue

    It does shut the heater off if the filter pump turns off and cannot turn on without the ump being on.

    Thanks again

  4. #4
    Join Date
    May 2013
    Location
    Newcastle, CA
    Posts
    5

    Default Re: Pool heater connection issue

    PoolDoc,

    Thanks for all of your help and advice. You confirmed what I thought and now the heater is controlled by the Jandy and works like a charm.

+ Reply to Thread

Similar Threads

  1. Pool Liner holes at Return Connection
    By Mitch401 in forum In-Ground Pool Construction and Repair
    Replies: 15
    Last Post: 07-05-2011, 03:31 PM
  2. Blown PVC connection
    By shadowman in forum In-Ground Pool Construction and Repair
    Replies: 4
    Last Post: 08-15-2008, 10:55 AM
  3. Pool Heater Wiring Issue
    By TexasPoolGuy in forum Pool Equipment & Operations
    Replies: 2
    Last Post: 08-01-2006, 12:32 AM
  4. Electrical Connection 115 vs 230 Volts
    By CJDahl in forum In-Ground Pool Construction and Repair
    Replies: 6
    Last Post: 07-26-2006, 07:39 PM
  5. Leaking Connection
    By CoffeeBean in forum In-Ground Pool Construction and Repair
    Replies: 8
    Last Post: 06-14-2006, 11:46 AM

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts