Is it possible that you have some flex PVC or other soft wall piping that may be collapsing under sufficient vacuum and time.
Is it possible that you have some flex PVC or other soft wall piping that may be collapsing under sufficient vacuum and time.
No flexible piping in the system. Oh I wish it were the obvious solution. dry skimmer, etc.... covered already though....
Those are the symptoms of cavitation and if a line is collapsing as Dave suggests or there is some sort of periodic blockage, increasing the return head would allow it to expand again (reduce the suction head). A suction gauge would help to confirm that.The noise which sounds like rocks clattering, is what I have read to be the sound of cavitation. So that may just be s symptom of the pressure drop and not the cause of it. One way I have found to make the noise stop is restrict the returns to cause the pressure to build up some. I dont leave it like that, just something I noticed.
Also, the video does not show the suction side plumbing very well. Do you have a check valve anywhere? Sometimes the flappers can break and cause similar symptoms.
Mark
Hydraulics 101; Pump Ed 101; Pump/Pool Spreadsheets; Pump Run Time Study; DIY Acid Dosing; DIY Cover Roller
18'x36' 20k plaster, MaxFlo SP2303VSP, Aqualogic PS8 SWCG, 420 sq-ft Cartridge, Solar, 6 jet spa, 1 HP jet pump, 400k BTU NG Heater
There is one check valve side after the filter and before the 8 tab chlrine feeder...
Ok... Towel, thrown... calling service....
For my sake, and especially, for Mark -- when you find out what the problem actually was, please let us know.
Yeah, all the input insight is appreciated.....
Extremely frustrated, as I've rebuilt engines, worked on 100,000 dollar laser medical printers.... and a freaking pool pump and some plumbing has me stumped....
It's gonna be a piece of dang mulch flying up and getting stuck in one of the T connectors and sinks back down whenever the pump shuts off, thats causing turbulance in the flow.... Something I cant see without cutting plumbing... And still tempted to do since one of the valve handles snapped off today (while opening it for the 100th time this week) . cheap junky 8 dollar ball valves.... But the grand wizards that built the thing butted all the connections in such a manner... I have to cut out all 4 valves on the suction side and redo the whole darn run...
There is not enough pipe space to splice....full redo...
https://fbcdn-sphotos-a.akamaihd.net...28470668_n.jpg
OK so where have things progressed...
Well two valve handles broke off so cut the plumbing up and replaced 4 junk ball valves. While the valves were out blew out the lines not much in the way of debris...
Set the new valves... cranked it up... purred like a kitten.... for about 30 minutes..... this was a pump that had been off for 2 days COLD........
air bubbles purged in a bout 5 minutes to a nice primed clear basket side.....
I wasnt paying anyone for valves and figured it would be a great time to remove any debris in the lines... The vavles were all suction, main drain, two skims, and vacum....
So seems to me if air related I would see air... The timing would be consistent.
The problem appears directly related to how long the pump has sat to get cold...
The pump itsel has had everything on the suction side replaced, gasket on the basket lid, gasket on the coupling to the valves, oring on diffuser, diffuser, impeller, wear ring, shaft seal... basically everything except the motor....
So when Pressure side is on 18-20 psi
vacuum is 6-7 in hg
ran for about 5 minutes before the noise and filter pressure dumps to about 10. basket vacuum drops to 1 or zero..
Another thing I notced this stops after I reseat the lid.... without waitig for a cool down... I replaced the oring but do the lids go bad? I cant see anything... I slathered the o ring really good with lube and got about 20 minutes of vacuuming before the noise started again. If there are air bubbles they are crazy small...
To vacuum just as I have done for 4 years:
Kill the two skimmers, turn cleaner valve on, to get the vacuum moving
While vacuuming the pressure stayed around 18 at the filter... vacuum climbed to 15 in hg at the basket. as a result of the skimmers off.
Then when the noise kicks in everything dives...
Lid Assembly? Any votes?