Re: New pool with electrical shock
Do you have the 1.4V between the ground and neutral busses in the Service Panel? These busses should (code around here) be strapped to each other in the service entrance panel (but not in any sub panel). Ground and neutral are also usually connected together in the meter pan where the neutral/ground connection connects neutral to the driven ground. I would make sure that neutral is properly electrically connected to ground in the service entrance panel and in the meter pan as this is important to the safety of the electrical circuits in your home. I'm not sure that adding additional driven grounds will help, it may worsen any ground loop problem.
Is the light supplied from the sub-panel that supplies all other pool-touching circuits?
Ben is right (of course) that bonding the entire pool, pool water, and pool area (including every bit of metal larger than 4") should alleviate any shock as everything swimmers touch will be at the same potential.