    Exclamation Electrical wiring concern with my PB

    I just had a conversation with my PB about how they are going to wire my EasyTouch 8 control panel. First a little background. I have a 42 slot 200 AMP main panel (just upgraded it myself from 125 AMP to allow for pool equipment, lighting, etc) with 6 slots left open. The controller we are using is the EasyTouch 8 that has a 125 AMP capable 16 slot sub panel built in. I want to save some slots in my main panel for dedicated 20 AMP and/or 50 AMP circuits for things like power tools and a welder, etc. I also wanted to mention my main breaker panel is about 5-6 feet from where my control panel will be.

    The electrician my PB uses wants to run a few individual runs (a few 30 and 15/20 AMP runs) to my control panel which would completely bypass the sub panel in the control panel. This solution would use 5-6 slots total from my main panel. By doing this it leaves me without any additional power for landscape lighting, etc at the control panel and basically would force me to run additional power to the control panel if I want to add landscape lighting or something else that would be controlled by the control panel.

    What I wanted to do was have them make a single 100 AMP run from the main breaker panel (100 AMP breaker in my main panel would only require 2 slots) to the control panel and run all the equipment from the sub panel built in. This would leave me with plenty of power for landscaping lighting, power to the outdoor kitchen, etc at the control panel. My understanding this is the normal way to do this. Most of the panels I saw from other PB's had their control panels wired this way.

    In order to do it my way they want to charge an extra $300.00. I was told this represents the cost for the extra breakers, wire, etc. It seems awfully excessive considering the multiple 30 AMP and 15 AMP runs would not be needed. The incremental cost here is larger wire (#4-#2 copper depending on what chart you use vs whatever would be needed for the other circuits (BTW #2 is $ .95 a foot so that is only $15.00 for the largest wire)) and the cost of the 100 AMP feeder breaker (about $35.00). It was also mentioned that larger conduit would be needed and that is harder to work with the larger wire. I am not so sure about how hard it is to deal with #2 copper. I just rewired my main panel with 4/0 aluminum and that is tough stuff to work with!

    I am not pissed at my PB at all but the situation really bothers me. To me it would seem the way they want to run it is not normal and is basically talking the easy way instead of doing it the right way. It seems like I am at the mercy of the electrician and that is part I hate. I want to push this issue but don't want to get into an adversely situation with my PB.

    What do you guys think? Thanks!

    Steve

  2. #2
    Join Date
    Dec 1969
    Location
    the woodlands, texas.
    Posts
    82

    Default Re: Electrical wiring concern with my PB

    Quote Originally Posted by skamp View Post
    It seems awfully excessive considering the multiple 30 AMP and 15 AMP runs would not be needed. The incremental cost here is larger wire (#4-#2 copper depending on what chart you use vs whatever would be needed for the other circuits (BTW #2 is $ .95 a foot so that is only $15.00 for the largest wire)) and the cost of the 100 AMP feeder breaker (about $35.00). It was also mentioned that larger conduit would be needed and that is harder to work with the larger wire. I am not so sure about how hard it is to deal with #2 copper. I just rewired my main panel with 4/0 aluminum and that is tough stuff to work with!
    I disagree. It's more affordable to use multiple breakers with a smaller gauge wire. However even though it's cheaper I'll always energize the pool's sub panel with the wire size I need for my load just to save the breaker spaces in the existing power center. If I were constructing your pool I'd use a #8 and if you wanted more power you'd have to pay for the upgrade in ampacity based on actual cost. It would be less than 100 bucks.

    The 300 he's asking isn't out of line, I'm certain it's exactly what his electrician is charging him. This is the difference between inhouse work and outsourced work by a subcontractor. He doesn't dictate his costs, the sub does.

    See ya,
    Kelly

  3. #3
    skamp is offline Registered+ Thread Analyst skamp 0
    Join Date
    Aug 2006
    Location
    Cypress, TX
    Posts
    94

    Default Re: Electrical wiring concern with my PB

    Quote Originally Posted by huskyrider View Post
    I disagree. It's more affordable to use multiple breakers with a smaller gauge wire. However even though it's cheaper I'll always energize the pool's sub panel with the wire size I need for my load just to save the breaker spaces in the existing power center. If I were constructing your pool I'd use a #8 and if you wanted more power you'd have to pay for the upgrade in ampacity based on actual cost. It would be less than 100 bucks.

    The 300 he's asking isn't out of line, I'm certain it's exactly what his electrician is charging him. This is the difference between inhouse work and outsourced work by a subcontractor. He doesn't dictate his costs, the sub does.

    See ya,
    Kelly
    Kelly,
    I absolutely agree it is cheaper to do it with more runs of smaller wires even though in my opinion it is the wrong way to do it. If there is a sub panel in the control panel it should be engerized. I also 100% agree that I should be responsible for the difference in cost. If they told me $100.00 more for the 100 AMP breaker, larger wire (2 AWG or 4 AWG vs multiple runs 10-14 AWG wire) and labor I would have no problem whatsoever even thouggh that is still a bit high (the reality is the 100 AMP breaker plus the larger wire is about $50-60 total without taking out the cost of the 14-12 AWG wire they won't need to use). I do have a serious issue with $300.00.

    I would have no problem paying the incremental cost but they claimed they spoke with the electrician and it would be $300.00 to wire a sub panel. They told me they normally do a sub panel if there is not enough room in the main panel. If that was the case I could understand as they would need to run wires back from the sub panel to the main panel to make up for the breakers that they used. This in not the case for me.

    I am not sure how to handle this with my PB. Should I tell them they are way out of line and talk to someone higher up like the owner? I really don't want to get into a fight with my PB as they have been great up to here but I don't think I should just suck it up and pay $300.00 for $50-100 worth of work. Thanks!

    Steve

  4. #4
    Join Date
    Dec 1969
    Location
    the woodlands, texas.
    Posts
    82

    Default Re: Electrical wiring concern with my PB

    I suggest just paying it.
    I really don't see the electrician coming down on his price, and I don't see the contractor making a concession out of his contract. He never made an allowance for it on his spread. The price the electrician is asking is the fair market value of the upgrade to 100 amps regardless of how much the additional materials cost.
    If he proceeds with his multiple breakers installation it's going to take 5 slots in your existing breaker box. It'll be 2 double throw 30's and a single throw 15 for the pool lamps.
    Another option would be to ask the builder if you purchased the materials would the electrician install it on your behalf, all he'd be out is the same labor it would of taken to begin with.

    See ya,
    Kelly

  5. #5
    skamp is offline Registered+ Thread Analyst skamp 0
    Join Date
    Aug 2006
    Location
    Cypress, TX
    Posts
    94

    Default Re: Electrical wiring concern with my PB

    Quote Originally Posted by huskyrider View Post
    I suggest just paying it.
    I really don't see the electrician coming down on his price, and I don't see the contractor making a concession out of his contract. He never made an allowance for it on his spread. The price the electrician is asking is the fair market value of the upgrade to 100 amps regardless of how much the additional materials cost.
    If he proceeds with his multiple breakers installation it's going to take 5 slots in your existing breaker box. It'll be 2 double throw 30's and a single throw 15 for the pool lamps.
    Another option would be to ask the builder if you purchased the materials would the electrician install it on your behalf, all he'd be out is the same labor it would of taken to begin with.

    See ya,
    Kelly
    Kelly,
    As always I appreciate your response. I really don't want to suck it up but it looks like I may have to do that. I will propose buying the supplies and see what they say. Thanks!

    Steve

  6. #6
    Join Date
    Dec 1969
    Location
    West, Texas
    Posts
    67

    Default Re: Electrical wiring concern with my PB

    Steve,
    I will throw my 2 cents in on this. First of all $300.00 is not out of line. Second, you need to determine what your panel is pulling now without the pool equipment on it. You say you have a 200 amp service correct? Well if you are pulling , lets say 150 amps now without your pool equipment then you do not have enough amperage to add a sub panel of 100 amps. But lets say you are only pulling 100 amps now then you do have enough amperage to add a 100 amp subpanel BUT you will not have enough left to add anything (like tools or welders) in the future from your panel. If you go over 200 amps then you run the risk of over loading your service. Your 4/0 wire is just at the 200 amp range so if you add more amperage then you run the risk of your service wire over heating and then you could run into a dangerous situation. If you will have over 200 amps total you will need to run the service from your meter to your controller panel and not from your existing panel. But to do this you need to make sure your meter is rated for more then 200 amps. Not sure if I wrote this to where you can understand what I am saying or if all I did was confuse you more.
    Boyd
    27' Round AG, 17,204 gallons, sand filter
    &
    Proud Father of an Army Soldier

  7. #7
    pinkivory_99 is offline ** No working email address ** pinkivory_99 0
    Join Date
    Dec 2005
    Location
    Galveston, Texas, USA.
    Posts
    9

    Exclamation Have it your way!!!!!

    I would push the issue. The reason you are installing the East Touch 8 is so you can control the equipment and acessories that you add in the future from this panel, plus if you have to work on pool equipment etc you can shut off the 100 amp breaker and not affect your household items.
    Setting it up with a 100 amp service would be the best way to do it and it should not cost 300.00. Wire size should be #2 enclosed in 1 1/4" or 1 1/2" grey pvc pipe and #2 wire is not that hard to work with. If it is a straight run from your box to the Easy touch it should be a piece of cake. Tell the pool builder that you will take care of it youself, sounds like you would be capable of doing this since you upgraded you main panel. The electrician could run the pool equipment etc. wiring out of the easy touch. Maybe the PB and electrician do not know how the Easy Touch works????? and this is why they do not want to use it.
    I don't think you will ever overload the 200 amp service, I run shop tools, 2 electric, kilns pool equipment and household loads and never have had a problem, you have to realize all of the electrical items in your house are not running at the same time.
    Stand your ground and get it the way you want it. You have to live with it the PB and electrician do not. Just my 2 cents.....

  8. #8
    Join Date
    Dec 1969
    Location
    West, Texas
    Posts
    67

    Default Re: Electrical wiring concern with my PB

    "I don't think you will ever overload the 200 amp service, I run shop tools, 2 electric, kilns pool equipment and household loads and never have had a problem, you have to realize all of the electrical items in your house are not running at the same time."

    Pinkivory,
    Although you are probably right,it is better to check then just assume and then find out you are screwed.
    Boyd
    27' Round AG, 17,204 gallons, sand filter
    &
    Proud Father of an Army Soldier

  9. #9
    Join Date
    Dec 1969
    Location
    the woodlands, texas.
    Posts
    82

    Default Re: Have it your way!!!!!

    Quote Originally Posted by pinkivory_99 View Post
    Tell the pool builder that you will take care of it youself.
    I disagree with this completely. You'll have no warranty for your first year from the electrician.

    Quote Originally Posted by pinkivory_99 View Post
    it should not cost 300.00.
    I'm curious, please tell me what you think it should cost.


    I do agree that it should be a 2awg in a 1 1/2" conduit.

    I also agree that energizing the 100 amp power center is really no big deal.
    If, by chance, you were amp'd out on your load you'd trip the 200 main disconnect breaker and lose all power everywhere until it was reset. 200 amps is a bunch and unless you had a heat pump on the pool running at the same time as an electric home heater, electric oven, and an electric clothes dryer, plus your usual lights and televisions etc.. I seriously doubt that you'd trip it.

    I really think the best bet is to ask the builder if you can purchase the materials and have his sub install them.

    See ya,
    Kelly

  10. #10
    Join Date
    Dec 1969
    Location
    West, Texas
    Posts
    67

    Default Re: Have it your way!!!!!

    Quote Originally Posted by huskyrider View Post
    I disagree with this completely. You'll have no warranty for your first year from the electrician.


    I'm curious, please tell me what you think it should cost.


    I do agree that it should be a 2awg in a 1 1/2" conduit.

    I also agree that energizing the 100 amp power center is really no big deal.
    If, by chance, you were amp'd out on your load you'd trip the 200 main disconnect breaker and lose all power everywhere until it was reset. 200 amps is a bunch and unless you had a heat pump on the pool running at the same time as an electric home heater, electric oven, and an electric clothes dryer, plus your usual lights and televisions etc..

    See ya,
    Kelly
    Kelly what you say may be true 99% of the time BUT that 1% of the time do you want to take the risk of the breaker NOT tripping and your wire over heating and possibly starting a fire? I wouldnt take that risk.My thinking is always do the job right, not the cheapest or easier way.

    And if someone tells him to do it his self then that is not a smart thing to tell him. Around here we have city codes, where you have to get permits and you have to be a licensed electrician , true a home owner can take a test and then do their own electrical work but being on a pool i would highly discourage a home owner from doing this.

    I would also be interested in hearing what the original poster and others think a fair price would be.
    Boyd
    27' Round AG, 17,204 gallons, sand filter
    &
    Proud Father of an Army Soldier

+ Reply to Thread

Similar Threads

  1. ADA compliant concern
    By Jimca in forum Commercial Pool Users, Managers & Workers
    Replies: 0
    Last Post: 02-12-2013, 07:30 PM
  2. Aqualink PDA-PS8 Wiring
    By VrRotate in forum In-Ground Pool Construction and Repair
    Replies: 1
    Last Post: 04-20-2012, 02:37 PM
  3. Help - Need information for wiring for an AGP
    By hudson.bh in forum Above-Ground Pool Construction & Repair
    Replies: 13
    Last Post: 06-09-2010, 09:40 AM
  4. Wiring a timer
    By hhkont in forum Pool Equipment & Operations
    Replies: 5
    Last Post: 06-02-2010, 08:40 AM
  5. Electrical SWG
    By Jeffery in forum Salt Generators (SWCG) & other Chlorine Feeders
    Replies: 1
    Last Post: 05-05-2006, 05:21 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts