KS, Welcome to the forum.
You should ideally plumb them in parallel and in addition put a bypass valve to divert some water around them. For efficient enough heating you don't need all the water going through them. With a pump that size you can probably divert 75% of the total water around them. The way to tell is to set the bypass so the temperature of the output of the solar heaters is just a couple degrees warmer than the input. If the output is too warm then close the bypass valve a little to get more water through the panels. You'll probably find doing it this way will result in very little pressure change. If it too clumsy to plumb in parallel then leave them in series, add the bypass, and apply the same reasoning to set the flow. Watermon has two 2x20s in series and they work just fine....with the bypass valve. She only sees about a 1-2 psi pressure change between full bypass and the setting for good panel flow.
Al
16'x32' oval 22K gal IG vinyl pool; ; Hayward S244T sand filter; Hayward superpump 1 HP pump; hrs; K-2006; PF:5.5