    Ok, I am not the sharpest knife in the draw, but I need some help understanding this.

    In the installation instructions it states:

    The solar system works best at flow rate of 1-4 gpm. To regulate flow, simply document the pressure on the pressure gauge of the filter with the by-pass valve open and the pump running. Then throttle the by-pass ball valve closed until the pressure on the filter gauge has increased more than the originally documented........Additional fine tuning may be required.

    Ok, how am I supposed to figure out the pressure increase on the filter gauge vs gpm flow thru the panels????

    I have 1 1/2" pool lines, a 1 hp hayward pump.

    Thanks for any insight you might have.

    TRHOD
    Ted (TRHOD) North Canton, Ohio
    1974 Anthony 24,000 gal IG vinyl, Hayward sand filter/1hp superpump. (5) 2x20ft sungrabber solar panel roof mounted
    Acquired pool June 2006 Been BBBing ever since

  2. #2
    Poconos is offline SuperMod Emeritus Whizbang Spinner Poconos 4 stars Poconos 4 stars Poconos 4 stars Poconos 4 stars Poconos 4 stars Poconos 4 stars
    Join Date
    Dec 1969
    Location
    Honesdale PA
    Posts
    1,812

    Default Re: Sungrabber solar panel flow rate calculation

    Simple answer is you can't calculate anything based on the vague setup information they gave you. With any kind of heat exchanger you get the maximum heat transfer at the maximum temperature differential. In the extreme limits, no flow would be a hot panel and at full flow a panel at pool water temperature. In the first case you get 0 BTU transferred to the pool because the flow is zero. The last case would result in the maximum BTU transfer to the pool but may restrict the flow unnecessarily. A BTU is the amount of heat needed to raise one pound of water one degree F. I would set the bypass valve to divert enough flow to the panel to result in a few degree F rise at the solar panel outlet in full sun. Nothing critical about this. Just using some numbers as an example with no idea how close they are, if no flow results in a panel temperature of 150 deg F and the water is at 75 deg F, you have a 75 deg differential. So what if the outlet is now 80 deg F. You still have a 70 deg differential so the efficiency penalty isn't much at all and you still maintain a good flow. From a pressure rise standpoint, see what the rise is with the bypass fully closed and that will give you an idea of the flow resistance the panel adds to the system. The lower the resistance the more flow you can put through the panel without taking a significant flow hit. It's all voodoo and whatever works best.
    I know I rambled but I hope this helps.
    Al

  3. #3
    Join Date
    Jun 2006
    Location
    Ohio, North Canton
    Posts
    43

    Default Re: Sungrabber solar panel flow rate calculation

    Al,

    thanks for your thoughts.

    I FINALLY got a couple of rainless days, and got the system hooked up last night and was able to give it a test run before dark.

    When I fully closed the bypass valve, my pressure only increased by 2psi. That didn't seem like a very big jump. I had contacted the solar panel company, who said if the rise in pressure was greater that 8psi from normal operating pressure, it would be hard on the pump.

    SO, still not sure about how to get the 1-4gpm optimal flow.

    1 thing I thought about doing was opening the return line from the solar panel and putting a 5gal bucket under it. Turn on the pump and pump water for 1 minute and measure how much water was pumped out of the panels. This should probably work, shouldn't it?? Then if I am over the 1-4gpm, just close the bypass valve about 1/2way and do the test again. Sound like a plan??
    Ted (TRHOD) North Canton, Ohio
    1974 Anthony 24,000 gal IG vinyl, Hayward sand filter/1hp superpump. (5) 2x20ft sungrabber solar panel roof mounted
    Acquired pool June 2006 Been BBBing ever since

  4. #4
    CarlD's Avatar
    CarlD is offline SuperMod Emeritus Vortex Adjuster CarlD 4 stars CarlD 4 stars CarlD 4 stars CarlD 4 stars CarlD 4 stars CarlD 4 stars
    Join Date
    Dec 1969
    Location
    North Central NJ
    Posts
    6,607

    Default Re: Sungrabber solar panel flow rate calculation

    It should, but really what you want is the maximum flow through the panels without straining the pump or risking damaging the panels (which usually isn't a problem).

    Here's a tip: If you think you need to slow down the water in the panels so it heats up more, that's wrong. All you are doing is preventing the movement of heat energy. Remember: It's all about HEAT transfer, not temperature. You want to maximize BTU output from your panels, not degrees and the more water you can safely move through the panels, the better! (There are some physical limits, such as cavitation of the water, but you'll never see them)

    If the water from the panels is flowing very strongly (and not crossing that 8psi limit) and the water from the panels is only slightly warmer than the pool, it's working and working well! If your pool is 75 and your panels are putting out 77deg, don't worry. When the water is 77, the panels will be 79 deg as they are EFFICIENTLY transferring heat energy to your water!

    I find that when the flow is too high, it's obvious because the skimmer and the main return just don't seem to be working too well. If I cut the flow to the panels and the skimmer and return improve, I know I had too much flow to the panels. You want to get it where the pool's plumbing is working well AND there is an ample flow through the panels.
    Last edited by CarlD; 05-14-2010 at 06:40 AM.
    Carl

  5. #5
    Poconos is offline SuperMod Emeritus Whizbang Spinner Poconos 4 stars Poconos 4 stars Poconos 4 stars Poconos 4 stars Poconos 4 stars Poconos 4 stars
    Join Date
    Dec 1969
    Location
    Honesdale PA
    Posts
    1,812

    Default Re: Sungrabber solar panel flow rate calculation

    Ted,
    The method you propose for measuring the flow will be close. The flow rate you measure will probably be a little on the high side because the panel outlet is now at zero pressure as opposed to something when it's connected on the other side of the bypass valve, but close enough. I think Carl said what I said but in simpler terms. Since your pressure only increased 2 psi with the bypass closed, that's good. Indicates little flow resistance in the panel. Even if you run that way you're toally OK. 8 psi rise? No.
    Al

  6. #6
    CarlD's Avatar
    CarlD is offline SuperMod Emeritus Vortex Adjuster CarlD 4 stars CarlD 4 stars CarlD 4 stars CarlD 4 stars CarlD 4 stars CarlD 4 stars
    Join Date
    Dec 1969
    Location
    North Central NJ
    Posts
    6,607

    Default Re: Sungrabber solar panel flow rate calculation

    Simple! That's me!
    Carl

  7. #7
    mas985's Avatar
    mas985 is offline Lifetime Member Whizbang Spinner mas985 3 stars mas985 3 stars mas985 3 stars
    Join Date
    Dec 2004
    Location
    Pleasanton, CA
    Posts
    1,423

    Default Re: Sungrabber solar panel flow rate calculation

    Based upon your other post, you have about 200 sq-ft of panels. I usually use a rule of thumb of about 1 GPM per 10 sq-ft of panels so in your case that would be 20 GPM total. That is the upper end of the range they gave you.

    You said that you have a 1 HP Hayward pump. Is that a 1 HP Superpump?

    Also, what is the actual pressure reading with and without solar?

    How high are the panels installed?

    Do you have separate suction lines coming to the pump?

    What size is the pipe for the solar panels?

    2 PSI rise could be reasonable for your setup but it depends on the answers to the above questions. However, forcing all of the water through the panels may not be necessary given you only need 20 GPM.
    Mark
    Hydraulics 101; Pump Ed 101; Pump/Pool Spreadsheets; Pump Run Time Study; DIY Acid Dosing; DIY Cover Roller
    18'x36' 20k plaster, MaxFlo SP2303VSP, Aqualogic PS8 SWCG, 420 sq-ft Cartridge, Solar, 6 jet spa, 1 HP jet pump, 400k BTU NG Heater

  8. #8
    Join Date
    Jun 2006
    Location
    Ohio, North Canton
    Posts
    43

    Default Re: Sungrabber solar panel flow rate calculation

    Quote Originally Posted by mas985 View Post
    Based upon your other post, you have about 200 sq-ft of panels. I usually use a rule of thumb of about 1 GPM per 10 sq-ft of panels so in your case that would be 20 GPM total. That is the upper end of the range they gave you.

    You said that you have a 1 HP Hayward pump. Is that a 1 HP Superpump?

    Yes it is a Hayward superpump 1HP pump.

    Also, what is the actual pressure reading with and without solar?

    [I]Pressure reading w/o panel is 20psi, with panels on (bypass valve fully closed) reading is 20psi. When I close the bypass valve the pressure will rapidly bump up to 25psi for a split second, then goes back down to 22psi[/I][

    How high are the panels installed?

    1 story house. The inlet line runs all the way up to the peak of the roof, then back down the south facing slow and ties into the panel at the bottom. The top of the return line from the panels is at the peak of the roof, and flows down the roof and back into the return line after the filter.

    Do you have separate suction lines coming to the pump?

    No, I have this plumbed in as follows. I put a T in the return line after the filter. This is the inlet to the solar panels. Approx 6" after the T on the return line from the filter, I installed the bypass valve. The return from the panels ties into the return line going to the pool approx 6" below the bypass valve.

    What size is the pipe for the solar panels?

    Headers are 1 1/2", all the plumbing I did was with 1 1/2" schedule 40 pvc.
    2 PSI rise could be reasonable for your setup but it depends on the answers to the above questions. However, forcing all of the water through the panels may not be necessary given you only need 20 GPM.
    Carl and Al, I get what you are saying now. Thanks.
    Ted (TRHOD) North Canton, Ohio
    1974 Anthony 24,000 gal IG vinyl, Hayward sand filter/1hp superpump. (5) 2x20ft sungrabber solar panel roof mounted
    Acquired pool June 2006 Been BBBing ever since

  9. #9
    mas985's Avatar
    mas985 is offline Lifetime Member Whizbang Spinner mas985 3 stars mas985 3 stars mas985 3 stars
    Join Date
    Dec 2004
    Location
    Pleasanton, CA
    Posts
    1,423

    Default Re: Sungrabber solar panel flow rate calculation

    20 PSI is really high for a 1 HP Superpump even with 1 1/2" plumbing. I would have expected much lower pressure. That is 50' of head for just the return side.

    Are you sure the gauge is operating properly? Does it go to zero with the pump off?

    Also, how long are the runs from pool to the equipment?

    Anyway it sounds like the panels will not fully prime unless the bypass is closed so you may need to operate that way. You might try to slowly close the valve until you hear the panels starting to prime and air coming out of the returns. This would be the minimum required flow setting but it probably wouldn't hurt anything to have all the water going through the panels.
    Mark
    Hydraulics 101; Pump Ed 101; Pump/Pool Spreadsheets; Pump Run Time Study; DIY Acid Dosing; DIY Cover Roller
    18'x36' 20k plaster, MaxFlo SP2303VSP, Aqualogic PS8 SWCG, 420 sq-ft Cartridge, Solar, 6 jet spa, 1 HP jet pump, 400k BTU NG Heater

  10. #10
    CarlD's Avatar
    CarlD is offline SuperMod Emeritus Vortex Adjuster CarlD 4 stars CarlD 4 stars CarlD 4 stars CarlD 4 stars CarlD 4 stars CarlD 4 stars
    Join Date
    Dec 1969
    Location
    North Central NJ
    Posts
    6,607

    Default Re: Sungrabber solar panel flow rate calculation

    Doesn't sound high to me. I have a Hayward 1 hp Superpump 2 spd and 20lbs is perfectly normal for 8 years now. When it hits 25 lbs I have to backwash. Since my solar panels are on a "Y" connection with the return, I don't see much of a change in pressure when they are on. My pump is only about 5' from the pool, and my return line is maybe 10' long and rises no more than 4' above the pump, plus another foot to the solar panels. I have 240 sq feet of panels.
    Carl

+ Reply to Thread

Similar Threads

  1. Flow rate sensor?
    By henryb in forum Pool Electronics
    Replies: 1
    Last Post: 08-31-2013, 02:51 PM
  2. PVC Maximum Flow Rate?
    By catnip in forum Pool Equipment & Operations
    Replies: 5
    Last Post: 03-14-2007, 12:15 PM
  3. Design flow rate vs maximum flow rate...
    By cruzmisl in forum Pool Equipment & Operations
    Replies: 5
    Last Post: 06-27-2006, 06:50 AM
  4. SunGrabber solar panel....
    By BullDean in forum Pool Equipment & Operations
    Replies: 13
    Last Post: 06-19-2006, 11:01 AM
  5. Two-speed pump flow rate
    By sharkey21 in forum Pool Equipment & Operations
    Replies: 1
    Last Post: 05-03-2006, 08:18 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts