    Ted,
    The method you propose for measuring the flow will be close. The flow rate you measure will probably be a little on the high side because the panel outlet is now at zero pressure as opposed to something when it's connected on the other side of the bypass valve, but close enough. I think Carl said what I said but in simpler terms. Since your pressure only increased 2 psi with the bypass closed, that's good. Indicates little flow resistance in the panel. Even if you run that way you're toally OK. 8 psi rise? No.
    Al

  2. #2
    CarlD's Avatar
    CarlD is offline SuperMod Emeritus Vortex Adjuster CarlD 4 stars CarlD 4 stars CarlD 4 stars CarlD 4 stars CarlD 4 stars CarlD 4 stars
    Join Date
    Dec 1969
    Location
    North Central NJ
    Posts
    6,607

    Default Re: Sungrabber solar panel flow rate calculation

    Simple! That's me!
    Carl

  3. #3
    mas985's Avatar
    mas985 is offline Lifetime Member Whizbang Spinner mas985 3 stars mas985 3 stars mas985 3 stars
    Join Date
    Dec 2004
    Location
    Pleasanton, CA
    Posts
    1,423

    Default Re: Sungrabber solar panel flow rate calculation

    Based upon your other post, you have about 200 sq-ft of panels. I usually use a rule of thumb of about 1 GPM per 10 sq-ft of panels so in your case that would be 20 GPM total. That is the upper end of the range they gave you.

    You said that you have a 1 HP Hayward pump. Is that a 1 HP Superpump?

    Also, what is the actual pressure reading with and without solar?

    How high are the panels installed?

    Do you have separate suction lines coming to the pump?

    What size is the pipe for the solar panels?

    2 PSI rise could be reasonable for your setup but it depends on the answers to the above questions. However, forcing all of the water through the panels may not be necessary given you only need 20 GPM.
    Mark
    Hydraulics 101; Pump Ed 101; Pump/Pool Spreadsheets; Pump Run Time Study; DIY Acid Dosing; DIY Cover Roller
    18'x36' 20k plaster, MaxFlo SP2303VSP, Aqualogic PS8 SWCG, 420 sq-ft Cartridge, Solar, 6 jet spa, 1 HP jet pump, 400k BTU NG Heater

  4. #4
    Join Date
    Jun 2006
    Location
    Ohio, North Canton
    Posts
    43

    Default Re: Sungrabber solar panel flow rate calculation

    Quote Originally Posted by mas985 View Post
    Based upon your other post, you have about 200 sq-ft of panels. I usually use a rule of thumb of about 1 GPM per 10 sq-ft of panels so in your case that would be 20 GPM total. That is the upper end of the range they gave you.

    You said that you have a 1 HP Hayward pump. Is that a 1 HP Superpump?

    Yes it is a Hayward superpump 1HP pump.

    Also, what is the actual pressure reading with and without solar?

    [I]Pressure reading w/o panel is 20psi, with panels on (bypass valve fully closed) reading is 20psi. When I close the bypass valve the pressure will rapidly bump up to 25psi for a split second, then goes back down to 22psi[/I][

    How high are the panels installed?

    1 story house. The inlet line runs all the way up to the peak of the roof, then back down the south facing slow and ties into the panel at the bottom. The top of the return line from the panels is at the peak of the roof, and flows down the roof and back into the return line after the filter.

    Do you have separate suction lines coming to the pump?

    No, I have this plumbed in as follows. I put a T in the return line after the filter. This is the inlet to the solar panels. Approx 6" after the T on the return line from the filter, I installed the bypass valve. The return from the panels ties into the return line going to the pool approx 6" below the bypass valve.

    What size is the pipe for the solar panels?

    Headers are 1 1/2", all the plumbing I did was with 1 1/2" schedule 40 pvc.
    2 PSI rise could be reasonable for your setup but it depends on the answers to the above questions. However, forcing all of the water through the panels may not be necessary given you only need 20 GPM.
    Carl and Al, I get what you are saying now. Thanks.
    Ted (TRHOD) North Canton, Ohio
    1974 Anthony 24,000 gal IG vinyl, Hayward sand filter/1hp superpump. (5) 2x20ft sungrabber solar panel roof mounted
    Acquired pool June 2006 Been BBBing ever since

  5. #5
    mas985's Avatar
    mas985 is offline Lifetime Member Whizbang Spinner mas985 3 stars mas985 3 stars mas985 3 stars
    Join Date
    Dec 2004
    Location
    Pleasanton, CA
    Posts
    1,423

    Default Re: Sungrabber solar panel flow rate calculation

    20 PSI is really high for a 1 HP Superpump even with 1 1/2" plumbing. I would have expected much lower pressure. That is 50' of head for just the return side.

    Are you sure the gauge is operating properly? Does it go to zero with the pump off?

    Also, how long are the runs from pool to the equipment?

    Anyway it sounds like the panels will not fully prime unless the bypass is closed so you may need to operate that way. You might try to slowly close the valve until you hear the panels starting to prime and air coming out of the returns. This would be the minimum required flow setting but it probably wouldn't hurt anything to have all the water going through the panels.
    Mark
    Hydraulics 101; Pump Ed 101; Pump/Pool Spreadsheets; Pump Run Time Study; DIY Acid Dosing; DIY Cover Roller
    18'x36' 20k plaster, MaxFlo SP2303VSP, Aqualogic PS8 SWCG, 420 sq-ft Cartridge, Solar, 6 jet spa, 1 HP jet pump, 400k BTU NG Heater

  6. #6
    CarlD's Avatar
    CarlD is offline SuperMod Emeritus Vortex Adjuster CarlD 4 stars CarlD 4 stars CarlD 4 stars CarlD 4 stars CarlD 4 stars CarlD 4 stars
    Join Date
    Dec 1969
    Location
    North Central NJ
    Posts
    6,607

    Default Re: Sungrabber solar panel flow rate calculation

    Doesn't sound high to me. I have a Hayward 1 hp Superpump 2 spd and 20lbs is perfectly normal for 8 years now. When it hits 25 lbs I have to backwash. Since my solar panels are on a "Y" connection with the return, I don't see much of a change in pressure when they are on. My pump is only about 5' from the pool, and my return line is maybe 10' long and rises no more than 4' above the pump, plus another foot to the solar panels. I have 240 sq feet of panels.
    Carl

  7. #7
    mas985's Avatar
    mas985 is offline Lifetime Member Whizbang Spinner mas985 3 stars mas985 3 stars mas985 3 stars
    Join Date
    Dec 2004
    Location
    Pleasanton, CA
    Posts
    1,423

    Default Re: Sungrabber solar panel flow rate calculation

    The reason I think it is high is because 20 PSI is about 49' of return head (adjusted for filter gauge height of 3') and if you assume another 5' of suction head, which is probably on the low side, results in 54' of total head loss. That pump puts out about 34 GPM @ 54' of head so the plumbing would be the equivalent of almost 800' of 1.5" pipe! To me it seems like a lot of head loss for such little flow rate. Also, the operating point is on the far left of the head curve which is far from optimum. If true, then there is something in the plumbing which is causing a lot of heat loss.
    Mark
    Hydraulics 101; Pump Ed 101; Pump/Pool Spreadsheets; Pump Run Time Study; DIY Acid Dosing; DIY Cover Roller
    18'x36' 20k plaster, MaxFlo SP2303VSP, Aqualogic PS8 SWCG, 420 sq-ft Cartridge, Solar, 6 jet spa, 1 HP jet pump, 400k BTU NG Heater

  8. #8
    Join Date
    Jun 2006
    Location
    Ohio, North Canton
    Posts
    43

    Default Re: Sungrabber solar panel flow rate calculation

    Quote Originally Posted by mas985 View Post
    20 PSI is really high for a 1 HP Superpump even with 1 1/2" plumbing. I would have expected much lower pressure. That is 50' of head for just the return side.

    Are you sure the gauge is operating properly? Does it go to zero with the pump off?
    Yes, the gauge is working. It goes to zero when pump is off, and I can see pressure changes when I back wash, turn on the solar panel lines, etc

    Also, how long are the runs from pool to the equipment?

    I'll try and give you my best guess estimate. The pool is 18X36. I have a skimmer line that I would say is 66-75', I have a wall drain I would say is 35'. My return line is a single line, and I would say it is 25-35'.

    Anyway it sounds like the panels will not fully prime unless the bypass is closed so you may need to operate that way. You might try to slowly close the valve until you hear the panels starting to prime and air coming out of the returns. This would be the minimum required flow setting but it probably wouldn't hurt anything to have all the water going through the panels.
    The panels DO prime. Actually, I have additional shut off valves going TO the solar panels, AND a shut off valve coming FROM the panels. When I open the shutoff valve TO the panels I can hear water moving thru the pipes and can see bubbles in the pool(air pushed out of panels before the water starts flowing), even before I turn the bypass valve on. So the panels are priming. As I start to turn the bypass valve, when I get it fully closed I will get a short bump in pressure from about 20-21 psi up to 25psi, the it rapidly returns to about 21-22psi.

    Today we had a partly sunny day, and I saw a 4-5 degree raise in the pool temp. It seems to me that it is working, but is it working to its full potential.

    One other side note that I can't figure out. When I start up the solar panels (open valves and flow water thru the panels) I have several glued joints that will leak. These are glued joints on the plumbing going TO the panels, and not the panels themselves) These are Drip leaks, not stream shooting leaks. When I go back out to the pool to shut the panels down at night, there are NO leaks and the concrete below the filter/pump, etc is dry.

    Why would the plumbing leak upon startup, but stop leaking thru out the day as water, pressure, and heat are applied to these joints???? This one is blowing my mind. I would think the heat, pressure, and water would cause the leak to get worse. This has happend the last 2 days I have run the panels. (keep in mind these are the only 2 days I have had the panels installed to run them)

    BLessings,
    Ted (TRHOD) North Canton, Ohio
    1974 Anthony 24,000 gal IG vinyl, Hayward sand filter/1hp superpump. (5) 2x20ft sungrabber solar panel roof mounted
    Acquired pool June 2006 Been BBBing ever since

  9. #9
    mas985's Avatar
    mas985 is offline Lifetime Member Whizbang Spinner mas985 3 stars mas985 3 stars mas985 3 stars
    Join Date
    Dec 2004
    Location
    Pleasanton, CA
    Posts
    1,423

    Default Re: Sungrabber solar panel flow rate calculation

    If the panels are only leaking when they are first turned on, then it could be the VRV. Sometimes they will let a bit of water through before shutting off. However, if you still see the water dripping after several hours of operation, then it is likely a very small leak somewhere. Just trace it back to it's origin to make sure.

    As for priming the panels. After all the air as stopped coming out of the returns with the bypass open (i.e. bypassing water around the panels), if you then close the bypass, is there any more air that is forced out of the panels? If not, then they are probably fully priming even when the bypass is on. However, if you get more air out, then the panels may not be fully priming.
    Mark
    Hydraulics 101; Pump Ed 101; Pump/Pool Spreadsheets; Pump Run Time Study; DIY Acid Dosing; DIY Cover Roller
    18'x36' 20k plaster, MaxFlo SP2303VSP, Aqualogic PS8 SWCG, 420 sq-ft Cartridge, Solar, 6 jet spa, 1 HP jet pump, 400k BTU NG Heater

  10. #10
    Join Date
    Jun 2006
    Location
    Ohio, North Canton
    Posts
    43

    Default Re: Sungrabber solar panel flow rate calculation

    The leak is NOT from the panels, it is from the plumbing (abs sch 40) glued fittings going TO the panels, but NOT the actual panels.

    The glued fittings will leak when I start moving water thru the pipes, but as the day goes on, the leaks will stop. This doesn't make sense to me.

    Why???
    Ted (TRHOD) North Canton, Ohio
    1974 Anthony 24,000 gal IG vinyl, Hayward sand filter/1hp superpump. (5) 2x20ft sungrabber solar panel roof mounted
    Acquired pool June 2006 Been BBBing ever since

+ Reply to Thread

Similar Threads

  1. Flow rate sensor?
    By henryb in forum Pool Electronics
    Replies: 1
    Last Post: 08-31-2013, 02:51 PM
  2. PVC Maximum Flow Rate?
    By catnip in forum Pool Equipment & Operations
    Replies: 5
    Last Post: 03-14-2007, 12:15 PM
  3. Design flow rate vs maximum flow rate...
    By cruzmisl in forum Pool Equipment & Operations
    Replies: 5
    Last Post: 06-27-2006, 06:50 AM
  4. SunGrabber solar panel....
    By BullDean in forum Pool Equipment & Operations
    Replies: 13
    Last Post: 06-19-2006, 11:01 AM
  5. Two-speed pump flow rate
    By sharkey21 in forum Pool Equipment & Operations
    Replies: 1
    Last Post: 05-03-2006, 08:18 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts