Re: two-speed with solar panels
Thanks for the excellent explanation. It's quite clear and I agree with everything except one part: the high-speed priming to fill the system. To be fully honest, I think that either what you say is wrong, or there is some factor at play that we haven't discussed.
It all boils down to this. To keep the valve closed, the pressure near the valve must be positive. I believe that pressure and flow completely describe the state of the system near the valve. To be concrete, suppose we have 2 psi and 40 GPM.
Suppose there is a diverter at the top that when turned, instead of sending the water to the panels, it sends it into a wide pipe going straight up for 4.6ft, open at the top. The pipe is wide so dynamic loss is negligible. We divert the flow. What happens?
In my book, the water goes up the open pipe and overflows, at an almost identical rate. The pressure near the valve is still about 2 psi (2 psi x 2.31 = 4.6 ft) and the flow is about the same. At the pump, there is no way of telling if the water is going through the panels or falls out of the pipe extension.
So it would seem that our pump (at low speed) is capable of lifting water to the valve, actually a bit higher than that, with plenty of flow. This pump, according to you, is not able to prime the system. Why? Sure, there is a period of transition as the pipe fills up. But the pressure at the pump can never be higher than when the pipe is full. Surely there is dynamic head, but that is also always less than when the pipe is full.
Then there is no need to prime at higher speed or power.
Joe's (joenj) contribution is revealing and made me realize that in fact there is one more variable we can play with: the jet diameter.
Just one foggy thought left for me. When my sand filter pressure goes up, needs a backwash, the panels do not stay full with water. You start to see bubbles in the returns and can hear the vacuum break opening/closing. This is my audiable alarm to backwash!
As Joe's filter gets more and more clogged, the after-filter pressure drops, the pressure at the top drops, finally becomes negative (or near there, depending on how the valve is built) and the valve opens. What happens then? The water on its way down (which is "responsible" for the negative pressure) flows at a higher rate that the pump can supply, and air is sucked in. As the amount of air in the pipe increases, there is less water in the pipe, consequently less weight. The suction drops (that is, pressure increases), and the valve closes again. The frequency of opening/closing depends on the hysteresis of the valve, and possibly other factors.
But the flow of the water on its way down can be reduced by narrowing the jet outlets. If you can live with the lower flow, that will make the system work again.
This also means that as you get close to zero pressure at the top, the dynamic loss on the down pipes is no longer relevant when computing the savings due to a lower flow. On the up pipes, it still is. (Sorry, I should explain this more clearly, but it's dinner time.)
I should say that it's VERY helpful to be able to have this kind of detailed discussions. I cannot thank enough all those involved.
Last edited by semenzato; 05-21-2007 at 12:08 AM.
30'x16' (irregular) indoor gunite/plaster pool, 10k gal,
Autopilot DLG-220 with SC-48 cell, 3/4 HP recirc pump,
solar panels, heat exchanger from 200 kBTU/hour Viessmann boiler