Peter, the first thing you need to be aware of is that local codes are often more strict than NEC, and sometimes have pretty unexpected requirements. Often, cities have a handout that outlines local codes. Also be aware that there are changes regarding pools in every revision of the NEC, and 2005 had many. These changes are mostly clarifications, because this stuff is confusing, and many electricians and inspectors don't understand it. Even if you are NEC 2005 to the letter, you may not be in compliance with local codes.Originally Posted by prh129
680 says no wiring with 5ft of the inside of the pool wall except for pool equipment feeds unless space or property lines make it necessary. For pool equipment wiring, 6 inches is the required depth for metal conduit, and 18 inches for non-metallic conduit. 680 does not make the exception for GFI. Although your 12 inch depth may meet article 300, it is in violation of 680.
It is my understanding that this requirement applies to all wiring in the pool area, even if it is not pool related and allowed by the space exception. Also, utility companies do not conform to NEC, but rather have their own code (NESC). If this affects you, contact your power company.
In a comment above, another poster stated that you shouldn't bond a double insulated pump motor. Per NEC 2005, the bonding wire must be installed, just not connected to the motor in the event a replacement motor is installed that requires bonding. These are primarily above ground pumps.
Bookmarks