I'm pulling three 10AWG and six 12AWG wires through about 30 feet of 3/4" nonmetallic conduit with two 90º standard radius turns.
I do have string strung through the conduit, so I can tie it off if needed.
...any tricks?
I'm pulling three 10AWG and six 12AWG wires through about 30 feet of 3/4" nonmetallic conduit with two 90º standard radius turns.
I do have string strung through the conduit, so I can tie it off if needed.
Not sure this was brought up before (I came in late), but I wired up my pool 4 years ago and spent a lot of time sorting out the codes.
One issue that has not been mentioned: if your pool pump is double insulated (most likely is), the bonding wire should not be attached to it.
(Yet the 2002 code says you should still keep in nearby just in case some day someone else installs a non-insulated pump ...)
I found the following web site useful:
http://www.selfhelpandmore.com/homew...bove/index.htm
And confirmed most of it myself with the 2002 NEC (I'm a EE PE, though I don't use the PE much for a living -- sorting out the pool stuff is the most code-intensive thing I've done)
Another issue regarding pool lighting:
The code for underwater lighting is really specific. Like requiring that conduit is run all the way to the box (not just the house), and that the circuit is not shared with anything else except pool lighting. It is by far the most underutilized 15A circuit in my entire house (just one AG pool light).
Raddish,
Regarding pulling your wire through the conduit, three things come to mind right away:
- 1: I don't have a "fill table" handy, but I think you -might- have too many wires in that 3/4 conduit. Double check the allowable fill for conduit.
-2: Instead of standard elbows on the conduit, you can/should use pulling elbows. It also -might- be required to use pulling elbows. Again, I don't have the tables/code handy to look it up.
- 3: Use wire pulling lube aka "snot".