Quote Originally Posted by NWMNMom
Can someone explain "bonding" and some of the wiring requirements, why that is all needed? We are getting an AG pool and have a GFI panel close by (20') so expect to plug in right to that. Are these pump/filter set ups supposed to be hard wired? We don't plan on pool lights - our merc vapor yard light is right next to the pool area.
Bonding is a wiring scheme that connects everything conductive associated with and near the pool so that it all remains at the same voltage if some electrical mishap occurs. You can only be shocked if you touch two things that are at different voltages, like the ground and a power line. Even if an electrical appliance fell into a properly bonded pool and the GFCI didn't trip, you wouldn't be shocked because everything you could touch would be the same voltage. (Any volunteers to prove it ) Bonding has nothing to do with the power system.

AG pumps are normally required to have twist-lock connectors, and the 20 ft won't meet code in some areas.

As to the light, if you want a pool full of bugs, you've found the answer. 15 years ago when we installed our first AG, it was about 30 ft from an outside light. It was bug city every morning. The best solution to lighting I've found is the citronella torches. Much more pleasant than anything electrical.