You are not aloneOriginally Posted by The Raddish
. Most electricians and pool installers don't get it either.
That is exactly what you do: bond all of the metal pieces together so none can be at a different voltage. You also have to bond any conductive part of electrical equipment that could or does contact the pool water even if not within 5 feet. That would be some pump motors, heaters, SWCs etc..Originally Posted by The Raddish
By pool circuit, do you mean the power circuit for the pool? If so, it is bad practice to ground an electrical system at more than one point. You wind up with current flowing through the earth. Voltage is different at different points, so if you tie them together with a ground system, weird things happen. If you mean the bonding system, the idea is to create that "equipotential plane" which means anything the swimmer can touch is at one voltage. It doesn't matter if that voltage is the same as your house power, because any voltage without a reference is just an arbitrary number. If there is one thing conductive that a swimmer can touch that is at a different potential, then they can be shocked. Grounding just doesn't enter the equation. Adding a ground rod can make the whole mess subject to stray voltage problems. There was a FPN (Fine Print Note) added to the 2005 Code stating "equipotential stray voltage bonding conductors aren't required to extend to any panelboard, service equipment, or an electrode."Originally Posted by The Raddish
You really need to refer to the 2005 NEC. It explains some of this much more clearly than 2002. You may also want to Google for 2008 proposals for 680, as there is more change coming.
Look at Table 680.10 for burial depths. Clearly 18" min inside the 5 foot area.