    Default Re: Pump Efficiency

    Mark,

    Thanks again for your wisdom and great advice. Before I got your response, I took a look at the IntelliFlow pump curves and came up with the following formula that tracks very, very well with the curves:

    Head = (RPM/350)^2 - (GPM^2)/470

    This essentially reduces to the formula you gave, if comparing two different Head/RPM combinations, assuming that the GPM is 0. The above is more accurate when there is a non-zero GPM, but because the curves are relatively flat this isn't a huge difference at low GPM.

    For the 4x160, I intentionally wanted to use different flow rates for solar on and off since the solar on required 48 GPM for its solar panel efficiency while the solar off had no such requirement so could use a lower GPM of 33 worst-case (i.e. 8-hours) and this lower GPM (and RPM) should result in lower power and energy cost. This assumed that I always ran the pump for 8 hours since that is how long the solar could effectively be used to heat the pool. I understand that a single flow rate is simpler, but it's also (somewhat) more expensive.

    For the full IntelliFlow, I can see how setting a single flow rate is easy (and I wouldn't need the IntelliComm in that case) and that the IntelliFlow can cut the runtime to only do a single turnover, but there could be a case where it goes for 5.5 hours without the solar and then turns off (because that's one turnover with the 48 GPM rate that I must have to make the solar efficient in case it comes on), but then the sun comes out and there won't be any solar heating because the pump is off. That's why I wanted to hook in to the solar as a "feature" to be able to force the pump on. So while I had two situations anyway (solar on and solar off), I figured to minimize the energy usage in the most extreme cases with two different GPM rates.

    I understand the simplicity of a single flow rate, but thought I'd get away with lower flow in the solar off times because, well, because I can. In fact, I don't have to limit myself to 8 hours in that case and can have the pump "enabled" for the full 24 hours since I know the solar won't get triggered except during the day while the pump could use a VERY low GPM over up to 24 hours until one turnover is achieved. What I don't know (yet) is at what point a low GPM becomes less energy efficient where the longer time takes more energy than is saved by the lower GPM (and lower frictional losses). I don't have a good formula for the "power" curves except that it's about 50% of output power (proportional to product of GPM and Head) above about 40 GPM at low RPM and above 80 GPM at the highest RPM (at very low RPM, efficiency goes to hell regardless of GPM -- probably due to electrical and motor efficiency losses, so clearly using a very low GPM does not make much sense).

    A leaf trap to the vacuum line -- BRILLIANT! Jeez, I wish I had thought of that, but am glad you did. It seems that the requirements for a vacuum unit are much less stringent (it would appear that they require 25 GPM) and I could probably then have an automatic valve switch to use the vacuum cleaner on suction (instead of the skimmer) and the flow rate could be set to whatever is needed for that feature (hopefully, the same 48 GPM that the solar uses would be sufficient, though this is cut down due to sharing the suction with the floor drains which are on a separate line until we get close to the pump; also, the line to the cleaner is 1.5" instead of 2" so the losses will be greater than on the floor drain line). If I wanted to figure out approximate flow rates for these two lines that are branched together at the suction side of the pump, how do I do that? I can estimate friction losses from the pipe, but how do I know what losses or restrictions there are at the floor drains and skimmer? I know that the negative pressure at the pump side must be the same between the two lines (though their GPM will clearly be different due to different line sizes) and can calculate the less negative pressure as I move through the line, but do I just assume no resistance at the opening to the pool and just assume the flow rates are related to the size of the line (i.e. assume the suction loss is the same in both lines and work backwards to calculate the GPM in each line that would make that happen)?

    In terms of using a robotic cleaner, I don't think I can get away with having a cord on our hardscape to go into the pool -- my wife is picky about those things. And removing the robot might be more of a pain, though maybe it's about the same as pulling out the pressure (or vacuum) cleaner -- right now we just put the line that was in the pool over onto our coping and keep the sweeper unit in the corner at the deep end while we use the pool. What problems do you have with your vacuum cleaner or using a vacuum line?

    Thanks for the explanation of priming. That makes perfect sense to me.

    I feel like breaking out singing, "I'm so excited....and I just can't hide it....I know, I know, I know, I know, I know I want IntelliFlo...I want IntelliFlo". OK, so my rhythm sucks.

    Richard
    Last edited by chem geek; 01-19-2007 at 10:45 PM.

  2. #2
    mas985's Avatar
    mas985 is offline Lifetime Member Whizbang Spinner mas985 3 stars mas985 3 stars mas985 3 stars
    Join Date
    Dec 2004
    Location
    Pleasanton, CA
    Posts
    1,423

    Default Re: Pump Efficiency

    Richard,

    Something does not look quite right with that equation. From the pumps perspective, GPM and Head are inversely proportionate while GPM and RPM should be proportionate. Also for the pump, GPM is the dependent variable and Head is the independent variable while for the plumbing system it is the opposite.

    Here is the way I would formulate the problem using first order approximations. Note that second order effects do create some error in this methodology.

    Starting with the pumping efficiency equation (note this is slightly different than the energy efficiency equation):

    Eff = Head * GPM / (BHP * 3960)

    and from pump affinity equations:

    Effective BHP = BHP(max) * (RPM / RPM(max)) ^ 3

    So solving for GPM

    GPM = A * (RPM / RPM(max)) ^ 3 / Head

    where A = (Eff * BHP (max) * 3960) but this can be solved for using the head curves for the pump. So for the 4x160, using 60' of head is about 100 GPM, A = 6000. A will vary some with head (second order effects) but for now we will ignore that. Also, we can test the formula for other RPMs. @ 2350 RPM and a Head of 40', GPM should be about 47. It's tough to tell from the chart but it looks about right. So this formula should work for all RPM and Head values of the pump.

    Now, your pool plumbing has the relationship of:

    Head = B * GPM^2

    Where B can be found from the operating head and GPM. For without solar, you originally gave the head and flow rates as 45' @ 90 GPM so B = 1 / 180.

    Combining the equations gives you

    GPM = (A / B) ^ (1/3) * (RPM/RPM(max)) = 0.02974 * RPM

    This is a single formula which characterizes both your pool and the pump together. Since the pump goes from 3450 to 400 RPM, your GPM should range from 12 up to 97 which is a great range to be able to operate over. Heck, I might go for one of these too. At the lowest rate, you could have a 24 hour turnover which is fantastic! You really never need to shut off the pump and when the solar goes on, you will just need to bump up the flow rate some. The value of B changes for solar so you can use the appropriate number. Also, if you need two turnovers a day, you can adjust the pump for 24 GPM and still run for 24 hours.

    Let us know what you end up with.
    Last edited by mas985; 01-20-2007 at 05:13 PM.
    Mark
    Hydraulics 101; Pump Ed 101; Pump/Pool Spreadsheets; Pump Run Time Study; DIY Acid Dosing; DIY Cover Roller
    18'x36' 20k plaster, MaxFlo SP2303VSP, Aqualogic PS8 SWCG, 420 sq-ft Cartridge, Solar, 6 jet spa, 1 HP jet pump, 400k BTU NG Heater

  3. #3
    chem geek is offline PF Supporter Whibble Konker chem geek 4 stars chem geek 4 stars chem geek 4 stars chem geek 4 stars
    Join Date
    Nov 2004
    Location
    California
    Age
    66
    Posts
    2,226

    Default Re: Pump Efficiency

    Hi Mark,

    GPM and Head go in opposite directions which is why there is the minus sign in my formula, but they cannot be inversely proportional since the pump curves show a positive non-zero head with a GPM of 0. This is where the pump is spinning just to generate equivalent pressure against the head -- or another way of looking at it is that as much water is pumped towards the head as is leaked backwards so that the net GPM is 0. Your formulas don't work for that, unless I'm misinterpreting them. The formula I gave almost exactly matches all the pump curves (within 1 or sometimes 2 feet of head) for both the full IntelliFlow and the IntelliFlow 4x160 (except the latter appears to have a mistake labeling the 750 RPM which appears to really be 950 RPM).

    Anyway, I'm going to call my pool contractor to see if they can do the work to replace my pump and I'll very likely go with the full IntelliFlow. I'll keep y'all posted as to my results after it gets installed.

    Thanks,
    Richard

  4. #4
    mas985's Avatar
    mas985 is offline Lifetime Member Whizbang Spinner mas985 3 stars mas985 3 stars mas985 3 stars
    Join Date
    Dec 2004
    Location
    Pleasanton, CA
    Posts
    1,423

    Default Re: Pump Efficiency

    Richard,

    Maybe I need to clarify my methodology a bit better. My original intent was to model your pool and pump together and not to match the entire pump curve. Pump curves handle both static and dynamic head but most pools have mostly dynamic head (i.e. pool is not much lower or higher than the equipment pad). Therefore, under normal operation after priming, you will never see a condition where the head is high but the flow is near zero. So I originally modeled the pump at maximum RPM and head between 60'-80'. This should be the range that your pool operates within at that RPM. I could have done a polynomial fit but it was unlikely to offer much more accuracy.

    However, going back over the formulation, I made an error calculating the constant A. At 60' of head, the pump puts out 136 GPM and not 100 GPM.

    To show how well the approximation holds, I made simple spread sheet. Here are the results:

    HTML Code:
    Head @ 3450 RPM	60	70	80	90
    Actual GPM	136	117	97	60
    Approximate GPM	137	117	102	91
    Richard's GPM	132	113	90	58
    
    Head @ 2350 RPM	28	32	37	42
    Actual GPM	93	80	66	41
    Approximate GPM	93	80	70	62
    Richard's GPM	90	77	61	40
    
    Head @ 1500 RPM	11	13	15	17
    Actual GPM	59	51	42	26
    Approximate GPM	59	51	45	40
    Richard's GPM	57	49	39	25
    The head ranges are scaled with RPM to stay withing the main part of each speed's head curve. So you can see that the approximate GPM is not too bad and good up to about 80 feet of head @ 3450 RPM. It is unlikely a pool would be much above that anyway. So both your's and my methods have errors but in different locations.

    The other thing I would change about the formulation is to make the constant A independent of RPM which would be

    GPM = A * RPM ^ 3 / Head (Pump Formula)

    Where now, A = Head * GPM / RPM^3 of a particular sample point from the head curve. This makes the formula good for a range of head and all RPM values.

    Also, the pool plumbing equation, Head = B * GPM ^2 comes from the Darcy-Weisbach hydraulics equation relationship between head and GPM so the accuracy is pretty good.

    So with the above corrections the new formula for your pool is

    GPM = (A/B)^(1/3) * RPM = .033 * RPM or a range of 114 GPM down to 13.2 GPM.

    I just wanted to make sure you understood what I did.


    I also want to add that using your pump formula along with the plumbing formula and solving for GPM:

    GPM = 1 / 350 / (B+1/470)^(1/2) * RPM or
    GPM = .033 * RPM which is the same as using my pump formula.
    Last edited by mas985; 01-21-2007 at 04:42 PM.
    Mark
    Hydraulics 101; Pump Ed 101; Pump/Pool Spreadsheets; Pump Run Time Study; DIY Acid Dosing; DIY Cover Roller
    18'x36' 20k plaster, MaxFlo SP2303VSP, Aqualogic PS8 SWCG, 420 sq-ft Cartridge, Solar, 6 jet spa, 1 HP jet pump, 400k BTU NG Heater

  5. #5
    chem geek is offline PF Supporter Whibble Konker chem geek 4 stars chem geek 4 stars chem geek 4 stars chem geek 4 stars
    Join Date
    Nov 2004
    Location
    California
    Age
    66
    Posts
    2,226

    Default Re: Pump Efficiency

    NOTE TO MODERATORS:

    Could you please move the posts from #14 (somewhat arbirtrary, but I think that's a decent break) on to this thread I started in The China Shop? We are getting more technical than we should be for the general forum, but I do want to continue the discussion in a "safe" place that won't scare off newbies. Any net results, simple rules, or other useful information will continue to be posted in this thread, but the mathematics of fluid dynamics and statics and pump efficiencies will be kept out of this thread and placed in The China Shop.

    Thanks,
    Richard

+ Reply to Thread

Similar Threads

  1. Filtering out dead algae and determining pool system efficiency...
    By Winglessflight97 in forum Pool Equipment & Operations
    Replies: 3
    Last Post: 05-09-2011, 10:21 AM
  2. Punp speed & SWCG Efficiency
    By RochesterMark in forum Salt Generators (SWCG) & other Chlorine Feeders
    Replies: 4
    Last Post: 06-24-2010, 09:45 PM
  3. Clorox High Efficiency bleach???
    By mariner09 in forum Using Chlorine and Chlorinating Chemicals
    Replies: 4
    Last Post: 05-05-2008, 05:22 PM
  4. Pump Efficiency, Head, Flow, and related technical info
    By chem geek in forum The China Shop
    Replies: 13
    Last Post: 02-01-2007, 11:39 PM
  5. Spa Heater Efficiency?
    By cygnusecks in forum Pool Equipment & Operations
    Replies: 1
    Last Post: 05-10-2006, 08:29 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts