    Quote Originally Posted by Poolidiot View Post
    3" is NOT deep enough, code wise or saftey wise and you did say kids were involved right? I would also put the wire in conduit (PVC) also for safety reasons. Think of it this way...what cost more? renting a ditcher that will dig rock or having a small child or anyone for that matter getting hurt all because you didnt want to rent the equipment to do it right?
    I COMPLETELY agree with this.

    I don't just apply this to underground near pools or ponds, I do it to all underground installations.

    I've never ran, and never will run, UF Romex underground without placing it in conduit. The only wire I'll ever run without conduit is low voltage lamp wiring.

    You could easily take a flat head shovel and waller your little trench wide enough for some 1/2" A&U (Grey sch 40 above and underground) electrical conduit without impacting the yard.

    The risk of your install may seem slight but it isn't. I've hit more unprotected underground wire, with a shovel, in a lifetime of building pools than you could ever imagine. It always seems to be that the current homeowner had no idea where the electrical devices outdoors wiring laid in the yard.
    Your friend may know where the energized wire is today, but I'm sure that they won't be telling the new buyer of the property at the title company during closing the sale to a new owner.


    just my .02

    see ya,
    Kelly

  2. #2
    Join Date
    Aug 2006
    Location
    Leander Texas
    Posts
    15

    Default Re: Electrical Question

    Thanks for all the input! Looks like I have a spring project coming up...
    Cornelious 16x26x52" AG
    Hayward Matrix 2spd 1HP 110V Pump
    Old Junky Sand Filter
    Jacuzzi Landslide 55 DE Secondary Filter
    1-1/2" Dow Pink Foam Bottom W/Foam Cove

  3. #3
    Join Date
    Nov 2004
    Location
    Norfolk, VA.
    Posts
    4

    Default Re: Electrical Question

    If you are going to go with 10 or even 12 gauge wire I would recommend using at least 3/4 inch PVC conduit, I just finished pulling 10 gauge wire through 1/2 inch PVC and it was a royal pain.

+ Reply to Thread

Similar Threads

  1. Pump/motor electrical question
    By tomdow2 in forum Pool Equipment & Operations
    Replies: 12
    Last Post: 05-21-2007, 02:10 PM
  2. Electrical question
    By mohawk in forum Pool Equipment & Operations
    Replies: 2
    Last Post: 02-21-2007, 05:14 PM
  3. Electrical Bonding
    By dave orso in forum In-Ground Pool Construction and Repair
    Replies: 7
    Last Post: 11-06-2006, 12:34 PM
  4. pool lighting/electrical question
    By ryanm in forum Pool Equipment & Operations
    Replies: 2
    Last Post: 07-04-2006, 06:04 PM
  5. Electrical SWG
    By Jeffery in forum Salt Generators (SWCG) & other Chlorine Feeders
    Replies: 1
    Last Post: 05-05-2006, 05:21 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts