Thread: Raypak Gas Heater

  1. #1
    Join Date
    Dec 1969
    Location
    .
    Posts
    3

    Default Raypak Gas Heater

    I have a Raypak gas heater 335,000 BTU and the heater exchnage tubes rotted away. The heater is only 3 years old raypak says it is due to low ph has anyone experienced this problem or something similar?

  2. #2
    Join Date
    Jun 2006
    Posts
    190

    Default Re: Raypak Gas Heater

    My Raypak rotted out too after only 4 years. It was a Versa II which apparently are notorious for the manifolds rotting out. I replaced it with a Sta-Rite and have been really happy so far.

  3. #3
    Join Date
    Dec 2004
    Location
    Sacramento, CA, USA.
    Posts
    123

    Default Re: Raypak Gas Heater

    Low pH will, indeed, eat the copper from your heat exchanger in very rapid order. I see this a lot on apartment and hotel/motel pools where high use makes good water chemistry a very difficult thing to control. It is also very common on fiberglass and vinyl-liner pools wher the pH tends to be low if not cared for regularly.

    High water velocity (pump too large) will also do a similar thing to the exchanger.

    These are both beyond the control of the manufacturer and would happen to any brand of heater.

  4. #4
    Join Date
    Dec 2004
    Location
    .
    Posts
    17

    Question Re: Raypak Gas Heater

    Are heatpumps less vulnerable than gas fired heaters to such corrosion due to low ph water ? I have a vinyl lined unheated pool and am looking to put in a heater this summer. Thanks.

  5. #5
    waste is offline PF Support Team Whizbang Spinner waste 3 stars waste 3 stars waste 3 stars
    Join Date
    Dec 1969
    Location
    S.E Maine
    Age
    58
    Posts
    1,765

    Default Re: Raypak Gas Heater

    Just a couple of pennies for all --- one of the main reasons I started going to the 'pool sites' is this same problem. What I've seen is that the pools that need a new heat exchanger (in some cases YEARLY ) is the reliance on tri- chlor feeders with ~ NO water testing nor maintenance

    Tri- chlor has a very low pH and it doesn't take long for it to become so low that the copper heat exchanger just gets dissolved by the acid water!

    BBB is IMO the best way to care for a pool, but if you use tri- chlor - at least do as Carl says and spend 2 min a day to check the pool (and if a # is 'out of whack' - ADJUST THE CHEMISTRY ACCORDINGLY!!!) A heat exchanger runs ~ $1300 - is 1/2 hour per week of your time worth more than that???
    Luv & Luk, Ted

    Having done construction and service for 4 pool companies in 4 states starting in 1988, what I know about pools could fill a couple of books - what I don't know could fill libraries

+ Reply to Thread

Similar Threads

  1. RayPak RHP100 Heatpump (pool heater) has a leak - with picture
    By CountryBumkin in forum In-Ground Pool Construction and Repair
    Replies: 1
    Last Post: 03-25-2013, 02:18 PM
  2. Raypak Heater won't start getting a SNS code
    By Dirt007 in forum Pool Equipment & Operations
    Replies: 1
    Last Post: 05-27-2012, 04:30 PM
  3. Question on Raypak 2100 Pool Heater
    By Canaligator in forum Pool Equipment & Operations
    Replies: 5
    Last Post: 06-26-2011, 09:35 PM
  4. Raypak 2100 335A digital heater not working, please help
    By stanthepoolman in forum Pool Equipment & Operations
    Replies: 2
    Last Post: 06-24-2011, 01:47 PM
  5. RayPak and Intellitouch i5
    By dchango in forum Pool Equipment & Operations
    Replies: 3
    Last Post: 10-23-2010, 10:31 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts