+ Reply to Thread
Results 1 to 8 of 8

Thread: interesting re: pool pump wire guage

Hybrid View

  1. #1
    matt4x4 is offline Lifetime Member Verb Herder matt4x4 2 stars matt4x4 2 stars
    Join Date
    Dec 1969
    Location
    .
    Posts
    819

    Default Re: interesting re: pool pump wire guage

    Your pump won't have a problem, BUT your wire will, the reason you put in a heavier guage wire over longer runs or for higher loads is because the 14 guage will heat up, won't be an issue the first year or two or three, but the insulation will become brittle due to the heat that's created in the wire - less heat will be created in the 12 guage in comparison and the insulation will therefore last way longer.
    Brittle insulation will lead to a short, a short can lead to a fire, a fire can lead to a homeless family or God forbid, something even worse.
    Don't mess with your families safety!

    Oh, BTW - if the existing wire is 7 years old allready and was possibly overloaded, it could already be brittle or very close to being a hazzard.

  2. #2
    tenax is offline Registered+ Widget Weaver tenax 0
    Join Date
    Jun 2006
    Posts
    445

    Default Re: interesting re: pool pump wire guage

    interesting stuff guys..if i ever do replace the motor, i will stick with max 3/4 hp as that is adequate. the run from the panel box i would say is maximum 30 ft. is that maybe why i've been able to get away with 14 guage? i can replace the 14 guage starting at the pool shed to the timer to the pump with the 12 guage, but not easy to replace the wire from the panel in my basement to the shed..would it be of benefit even if i only replace the 14 guage from where it comes in shed>timer>pump with 12 guage and leave the other 14?

  3. #3
    Poconos is offline SuperMod Emeritus Whizbang Spinner Poconos 4 stars Poconos 4 stars Poconos 4 stars Poconos 4 stars Poconos 4 stars Poconos 4 stars
    Join Date
    Dec 1969
    Location
    Honesdale PA
    Posts
    1,812

    Default Re: interesting re: pool pump wire guage

    Some facts:

    From copper wire tables #14 is 2.58 ohm / 1000', #12 is 1.62

    That's .00258 / .00162 ohm per foot respectively.

    For a 30' run (60' of wire) that's .155 / .097 total ohms respv.

    I'm assuming a 120 V circuit with a 1/2 HP pump that draws 10 amps. Rough WAG here but erring on the conservative high side.

    That's a voltage drop of 1.55 / .97 V respv.

    Power loss is E**2 / R or I**2 * R or 15.5W / 9.7W respv.

    That power loss works out to be .52 / .32 Watts per foot of heating.

    Conclusions:
    With #14 you're wasting 5.8 watts of power.
    I don't feel the additional heating is significant.
    Cost delta of #12 vs #14 is small.
    Go with #12. Even on the partial run.
    If this is underground use UFB for underground direct burial, or a conduit.

    Hope I did all the math right.
    Al



    .

  4. #4
    GTakacs is offline Registered+ Thread Analyst GTakacs 0
    Join Date
    Apr 2006
    Posts
    51

    Default Re: interesting re: pool pump wire guage

    For 30ft of wire, 14 AWG is fine for a 3/4 hp motor. If you're running it at 110V it's still file. If you want a bigger pump you should consider running them off of 230V. If you're already running 230V then 14 AWG will handle all the way up to a 2hp pump at a distance of 30'.

    I have 10 AWG running from my breaker to my pool equipment for 230V plus a 14 AWG neutral if I need 110V over there.

  5. #5
    tenax is offline Registered+ Widget Weaver tenax 0
    Join Date
    Jun 2006
    Posts
    445

    Default Re: interesting re: pool pump wire guage

    thanks again guys..i think i'm good..the run is actually 25 ft..it's on 120 w/ a 15amp breaker that powers the pump exclusively. i have no intention to get it to share with anything else. i have 3 other 120 volt lines available to the shed so no need. the one speed motor draws 8.6 amps at full load and 120 volts.

  6. #6
    cwstnsko is offline Registered+ Thread Analyst cwstnsko 0
    Join Date
    May 2006
    Location
    Mesa, AZ
    Age
    60
    Posts
    117

    Default Re: interesting re: pool pump wire guage

    about a month ago I helped a friend drain and refill his pool (due to too high of CYA and CH.) About an hour into the draining, we started hearing a popping sound from over by the pump. After a couple of more pops, the motor shut down. After shutting down the power at the main panel, we discovered that the pump had been wired with 14 gauge solid wire (in 1988.) Over the years, the combination of current and vibration cause the wire to blow itself in two about 2 inches from the motor.

+ Reply to Thread

Similar Threads

  1. Damaged pool light conduit; broken bond wire
    By calitriv in forum Pool Equipment & Operations
    Replies: 6
    Last Post: 05-22-2012, 11:53 AM
  2. Remove pressure guage from filter?
    By Tishabiondy@natlmail.com in forum Pool Startup, Shutdown, & Winter Operation
    Replies: 5
    Last Post: 10-21-2007, 07:45 PM
  3. Extending pool motor bond wire
    By sharknj in forum Pool Equipment & Operations
    Replies: 2
    Last Post: 07-04-2007, 10:36 PM
  4. Bonding Wire
    By anotherpyr in forum In-Ground Pool Construction and Repair
    Replies: 2
    Last Post: 06-18-2007, 10:47 PM
  5. Is Pressure guage important?
    By ePoolUser in forum Pool Equipment & Operations
    Replies: 10
    Last Post: 05-15-2007, 01:44 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts