    Default Re: Electrical for pool

    Yes. Do as much as possible yourself. I always do all my own work. You save soo much money.

    Check with the city to see what depth you need to bury your conduit. They should have all the guidlnes for you. When my bro in law did his he used metal conduit and only had to go 8" in the ground. I used plastic and had to go 18".

  2. #2
    Join Date
    Apr 2006
    Location
    OC, CA
    Posts
    18

    Default Re: Electrical for pool

    I would run 4- #6awg thhn wires (2-blk, 1-wht, 1-grn) in a 1" schedule 40 PVC gray conduit. Do not exceed 360deg in bends atleast 18" deep. Install it on a 60amp breaker in your existing main panel. Use the same mfg breaker as your existing panel. Mount a 12/24 outdoor main lug subpanel. Any conduit above ground may have to be schedule 80. You should be able to run sealtight (gray liquid-tite flex) to your motors. Try not to run the sealtight over six feet. If you do not want to spend the money on a GFI breaker for the light mount a outdoor box underneath the panel with a GFI in it and run conduit to your light from there.
    John..

  3. #3
    matt4x4 is offline Lifetime Member Verb Herder matt4x4 2 stars matt4x4 2 stars
    Join Date
    Dec 1969
    Location
    .
    Posts
    819

    Default Re: Electrical for pool

    To answer your innitial question, no, you do not need to run a second line from the house, the sub panel, if installed off the main panel correctly will allow you to hook up as many breakers/individual circuits as it will accomodate.

  4. #4
    Join Date
    May 2006
    Posts
    47

    Default Re: Electrical for pool

    thanks for all the input. Any body have pictures of their subpanel setup. thanks chris
    Blding 18x36 IG vinyl rectangle with custom inpool steps, 22,000 gallons. Chris In Chapel Hill, NC us7sail@earthlink.net

  5. #5
    MarkC is offline Registered+ Weir Watcher MarkC 1 star
    Join Date
    Dec 1969
    Location
    .
    Posts
    178

    Default Re: Electrical for pool

    Here is the panel I used. http://www.intermatic.com/?action=prod&pid=8849 The 2 timers are for the pool sweep and the main pump. The panel excepts breakers right inside and I also have a GFI breaker in there that runs a convenience outlet (weatherproof cover) located in a small box directly under the Intermatic panel.

  6. #6
    Join Date
    May 2006
    Posts
    47

    Default Re: Electrical for pool

    Thanks for the info Mark. Who did you purchase the intermatic through? how much power do you have running to the panel?
    Blding 18x36 IG vinyl rectangle with custom inpool steps, 22,000 gallons. Chris In Chapel Hill, NC us7sail@earthlink.net

Closed Thread

Similar Threads

  1. New pool with electrical shock
    By Jose263 in forum In-Ground Pool Construction and Repair
    Replies: 8
    Last Post: 09-05-2011, 12:01 AM
  2. Electrical costs for my pool
    By rpoldervaart in forum Pool Equipment & Operations
    Replies: 27
    Last Post: 07-20-2006, 12:30 PM
  3. pool lighting/electrical question
    By ryanm in forum Pool Equipment & Operations
    Replies: 2
    Last Post: 07-04-2006, 06:04 PM
  4. Electrical outlets around pool.
    By beary in forum In-Ground Pool Construction and Repair
    Replies: 2
    Last Post: 05-09-2006, 11:10 AM
  5. New electrical subpanel for IG pool
    By Zaphod in forum Pool Equipment & Operations
    Replies: 4
    Last Post: 04-30-2006, 11:17 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts