Yes, the gauge goes to zero when the pump is shut off. I replaced the pressure gauge when I rebuilt the filter. Is it possible that the wet end has the impeller for a 1.5 hp pump?
Are you saying my setup has a 54' head?
Thanks
Yes, the gauge goes to zero when the pump is shut off. I replaced the pressure gauge when I rebuilt the filter. Is it possible that the wet end has the impeller for a 1.5 hp pump?
Are you saying my setup has a 54' head?
Thanks
21000 gal IG - 16x32 Vinyl Liner - Hayward 1HP pump - Hayward S244T Sand filter - Booster pump w/Polaris 280 cleaner - Pentair Rainbow 320 Chlorine Feeder - Taylor Test Kit K-2006C - Borate 50ppm - Salt 2400ppm - BBB all the way!!
Not unless the motor was up sized as well. Up sizing the impeller without up sizing the motor will overload the motor and trip the thermal limiter switch.
Yes, that is my best estimate based upon the filter pressure and the suction side plumbing layout.Are you saying my setup has a 54' head?
Mark
Hydraulics 101; Pump Ed 101; Pump/Pool Spreadsheets; Pump Run Time Study; DIY Acid Dosing; DIY Cover Roller
18'x36' 20k plaster, MaxFlo SP2303VSP, Aqualogic PS8 SWCG, 420 sq-ft Cartridge, Solar, 6 jet spa, 1 HP jet pump, 400k BTU NG Heater
So it looks like I should leave well enough alone as far as the pump goes. Is the pressure I am seeing at my filter what you would expect? If not, is it higher or lower than you would expect? Thanks again.
21000 gal IG - 16x32 Vinyl Liner - Hayward 1HP pump - Hayward S244T Sand filter - Booster pump w/Polaris 280 cleaner - Pentair Rainbow 320 Chlorine Feeder - Taylor Test Kit K-2006C - Borate 50ppm - Salt 2400ppm - BBB all the way!!
As I posted earlier, the pressure seems to be a bit high which means that there is more head loss in the return plumbing than would normally be expected for that setup. It could be the filter or anything after the filter.
Mark
Hydraulics 101; Pump Ed 101; Pump/Pool Spreadsheets; Pump Run Time Study; DIY Acid Dosing; DIY Cover Roller
18'x36' 20k plaster, MaxFlo SP2303VSP, Aqualogic PS8 SWCG, 420 sq-ft Cartridge, Solar, 6 jet spa, 1 HP jet pump, 400k BTU NG Heater
mas,
Would you recommend him tapping into the system in a few different points to determine where the back pressure is? Maybe one between the filter and heater and then one after the heater.
skeeter
That is a bit invasive and could cause other issues. However, a picture of the pad equipment might be useful to narrow it down some. Check valves, filters and backwash valves have all been know to cause problems with high pressure. Not to mention an incorrect valve setting.![]()
Mark