    Default Re: Super II Pump Replacment Decision

    Hi there. I hope I'm not reviving a thread no one cares about, but I thought I should update you, as I received my pump today. A lot of what we discusses was wrong. It turns out Hayward gave me wrong answers, too. Only the Inyo chart I linked (and used to make my hasty purchase decision) was right after all. The pump I received is a SP3010EEAZ. 1 HP, SF 1.5, THP 1.5. The motor model is SP1610Z1BE. Max amps is 14.6/7.3 after all. Now, all the charts and tables say this will give me the same performance as the 1.5HP/1.0SF SP3010X15AZ (motor UST 1152; max amps 18.6/9.3) at a lower amp draw. In theory, wouldn't that save about 25% energy (that's what I thought when I pushed the "buy" button)? Anyway, no matter who I asked except Inyo said max amp draw was identical, and it's not. I'm going to email you pictures of the old and new motor labels. If I could have one more minute of your time, before I have it installed, I would appreciate it if you could confirm that I will be OK using this new pump and also whether I can still put my old motor back on later (if I still choose to do so.) Reason for asking is that there are 3 other numbers different on the label, and I don't know if they mean anything or not. First, the "kW" number is .75 on the new motor, not listed on old, but online found it might be 1.1. Second, the new motor says "CODE L", the old one "CODE H". And third, the new one says "Thermal Protected CET50ABN" and the old one "CET40ABM". Thanks, appreciate it, and hopefully contributed something by sharing the actual label!

  2. #2
    PoolDoc's Avatar
    PoolDoc is offline Administrator Quark Inspector PoolDoc 5 stars PoolDoc 5 stars PoolDoc 5 stars PoolDoc 5 stars PoolDoc 5 stars PoolDoc 5 stars PoolDoc 5 stars
    Join Date
    Jan 2005
    Location
    Georgia
    Posts
    11,386

    Default Re: Super II Pump Replacment Decision

    Here's the rule I found on the AO Smith site: if the old motor's HP x it's Service Factor (SF) equals OR is less than the NEW motor's HP x SF, you're OK. If the new motor's multiple is LESS than the old motor's, you are NOT OK, and will need to replace the impeller.

    Looking at the photos you sent, what I'm seeing is:
    OLD => 1.5hp x 1.0 SF = 1.5
    NEW => 1.0hp x 1.5 SF = 1.5

    So, I think you'll be OK. About any of the other, I'm not sure.

+ Reply to Thread

Similar Threads

  1. Most energy efficient pool pump replacment
    By poodlepal in forum --cleanup--
    Replies: 0
    Last Post: 01-03-2013, 11:00 PM
  2. Hayward Super Pump is Super Noisy
    By moneypitpool in forum In-Ground Pool Construction and Repair
    Replies: 6
    Last Post: 07-25-2011, 10:16 AM
  3. Hayward Super Pump - Super Hot and Shutting Off
    By CapitalBoo in forum Pool Equipment & Operations
    Replies: 0
    Last Post: 06-18-2011, 09:32 AM
  4. Hayward Super Pump Really Hot...HELP?
    By calamtykel in forum Pool Equipment & Operations
    Replies: 6
    Last Post: 06-14-2009, 04:30 PM
  5. Pump seal for Hayward super pump?
    By goosegunner in forum Pool Equipment & Operations
    Replies: 1
    Last Post: 05-22-2006, 01:34 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts