Thread: 2 speed pump trips breaker

Hybrid View

  1. #1
    Join Date
    Jul 2006
    Location
    Northeast PA
    Posts
    11

    Default Re: 2 speed pump trips breaker

    Thanks for the replies...its not actually my pool...but a customers...in order to read the voltages....I had to disconnect the wires from the pump itself....cause otherwise it trips the breaker instantly....so I dont believe its the terminal block on the pump....that seems to be ok....the customer bought a pentair control system with a 2 speed relay and installed the system himself....he claims that the 70 volts applied to the not used windings shouldn't be a problem....I think differently....customer claims the pentair system is 100% wired correctly.....guess we'll have to check....my question was the 70 volts....sounds like the above post agree with me....by the way....this customer claims to be an electrical engineer.

  2. #2
    BigDave's Avatar
    BigDave is offline Lifetime Member Whizbang Spinner BigDave 3 stars BigDave 3 stars BigDave 3 stars
    Join Date
    Jul 2010
    Location
    New Jersey
    Posts
    1,932

    Default Re: 2 speed pump trips breaker

    Electrical theory and the trade practice of Electricians are different and often not mutually understood. Power Systems Engineers should understand that unbalanced loads and neutral faults and opens (in the customer premises as well as the mains and distribution networks) can cause unexpected voltages on neutral and lines. Neutral should be connected to Ground at the service entrance panel so voltage on the power company neutral could be seen on the Ground line.

    I'd want to know what the line to line and line to ground voltages are on this circuit with the control system disconnected.

    Bottom line - something's wrong. A good Electrician with pool experience should be able to help.
    12'x24' oval 7.7K gal AG vinyl pool; ; Hayward S270T sand filter; Hayward EcoStar SP3400VSP pump; hrs; K-2006; PF:16

  3. #3
    Watermom's Avatar
    Watermom is offline SuperMod Emeritus Quark Inspector Watermom 4 stars Watermom 4 stars Watermom 4 stars Watermom 4 stars Watermom 4 stars Watermom 4 stars
    Join Date
    Dec 1969
    Location
    Charleston, WV
    Posts
    9,345

+ Reply to Thread

Similar Threads

  1. Pump popping breaker.
    By 737Mech in forum Pool Equipment & Operations
    Replies: 1
    Last Post: 06-13-2012, 11:38 PM
  2. New Whisperflo Trips Breaker
    By jzerf in forum Pool Equipment & Operations
    Replies: 11
    Last Post: 07-27-2008, 09:59 AM
  3. 2 Spd pump trips breaker in high spd only
    By posguy in forum Pool Equipment & Operations
    Replies: 1
    Last Post: 06-07-2006, 07:56 PM
  4. GFI Breaker trips when I use the outlet
    By RENOPOOL in forum Pool Equipment & Operations
    Replies: 6
    Last Post: 05-23-2006, 08:49 PM
  5. pump trips ground fault breaker..
    By turnerd in forum Pool Equipment & Operations
    Replies: 2
    Last Post: 05-23-2006, 01:42 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts