Thread: 2 speed pump trips breaker

Hybrid View

  1. #1
    Join Date
    Jul 2006
    Location
    Northeast PA
    Posts
    11

    Default 2 speed pump trips breaker

    Hi....I have a Hayward Max-Flo II 2 speed pump that trips the breaker instantly when turned on....I have 250 volts between the common and high speed wires during high speed operation....but also have about 70 volts between the common and low speed wires....this is when it's in high speed.....when I switch the speeds....i still have approximately 70 volts applied to the pumps windings that aren't being used....is this normal....not sure if it is....reason for asking is because I've burned up 2 pumps in less than a year....I didn't do the electrical...the labels on the outside of the motor are burnt....like if the motor is getting extremely hot....any ideas???

  2. #2
    drband's Avatar
    drband is offline Lifetime Member Thread Analyst drband 0
    Join Date
    Dec 2004
    Location
    Gainesville, GA
    Posts
    84

    Default Re: 2 speed pump trips breaker

    Does not sound good. Some folks on the forum have pump wiring expertise and may be able to help. From you report, it sounds like there is a wiring fault in either the supply lines or even the terminal block on the pump itself. I did wire my own 2 speed but did not run into the problem you state. Maybe time to call an electrician.
    10,000 gallon IG vinyl liner pool, BBB user, salt added to 2300 ppm (because it makes the water feel great!), new liner/new water on 6/23/11, algae-free since 2006 (at least that's as far back as I remember). 1HP Hayward 2-SPEED CONVERTED Superpump, Hayward sand filter, PS234 test kit.
    Goal: To remain completely algae-free for the life of this new liner!
    Life lesson: It is what it is.


    12'x24' oval 9K gal IG pool; bleach; Hayward 244T sand filter; Hayward Super pump, 1 HP, 2-speed pump; 24hrs on low speedhrs; PS234; utility water; summer: ; winter: ; android phone; PF:13

  3. #3
    BigDave's Avatar
    BigDave is offline Lifetime Member Whizbang Spinner BigDave 3 stars BigDave 3 stars BigDave 3 stars
    Join Date
    Jul 2010
    Location
    New Jersey
    Posts
    1,932

    Default Re: 2 speed pump trips breaker

    I agree with drband - this is not good. Kinda sound like you might have a neutral and hot leg crossed. Is it fed from a GFCI breaker? Anything else on the circuit? Was this installed by a licensed electrician? Is the pump attached via a power cord or hard-wired? Is there a control system of any type on the same circuit?

    Best bet - find a different electrician, licensed with pool experience.
    12'x24' oval 7.7K gal AG vinyl pool; ; Hayward S270T sand filter; Hayward EcoStar SP3400VSP pump; hrs; K-2006; PF:16

  4. #4
    Join Date
    Jul 2006
    Location
    Northeast PA
    Posts
    11

    Default Re: 2 speed pump trips breaker

    Thanks for the replies...its not actually my pool...but a customers...in order to read the voltages....I had to disconnect the wires from the pump itself....cause otherwise it trips the breaker instantly....so I dont believe its the terminal block on the pump....that seems to be ok....the customer bought a pentair control system with a 2 speed relay and installed the system himself....he claims that the 70 volts applied to the not used windings shouldn't be a problem....I think differently....customer claims the pentair system is 100% wired correctly.....guess we'll have to check....my question was the 70 volts....sounds like the above post agree with me....by the way....this customer claims to be an electrical engineer.

  5. #5
    BigDave's Avatar
    BigDave is offline Lifetime Member Whizbang Spinner BigDave 3 stars BigDave 3 stars BigDave 3 stars
    Join Date
    Jul 2010
    Location
    New Jersey
    Posts
    1,932

    Default Re: 2 speed pump trips breaker

    Electrical theory and the trade practice of Electricians are different and often not mutually understood. Power Systems Engineers should understand that unbalanced loads and neutral faults and opens (in the customer premises as well as the mains and distribution networks) can cause unexpected voltages on neutral and lines. Neutral should be connected to Ground at the service entrance panel so voltage on the power company neutral could be seen on the Ground line.

    I'd want to know what the line to line and line to ground voltages are on this circuit with the control system disconnected.

    Bottom line - something's wrong. A good Electrician with pool experience should be able to help.
    12'x24' oval 7.7K gal AG vinyl pool; ; Hayward S270T sand filter; Hayward EcoStar SP3400VSP pump; hrs; K-2006; PF:16

  6. #6
    Watermom's Avatar
    Watermom is offline SuperMod Emeritus Quark Inspector Watermom 4 stars Watermom 4 stars Watermom 4 stars Watermom 4 stars Watermom 4 stars Watermom 4 stars
    Join Date
    Dec 1969
    Location
    Charleston, WV
    Posts
    9,345

+ Reply to Thread

Similar Threads

  1. Pump popping breaker.
    By 737Mech in forum Pool Equipment & Operations
    Replies: 1
    Last Post: 06-13-2012, 11:38 PM
  2. New Whisperflo Trips Breaker
    By jzerf in forum Pool Equipment & Operations
    Replies: 11
    Last Post: 07-27-2008, 09:59 AM
  3. 2 Spd pump trips breaker in high spd only
    By posguy in forum Pool Equipment & Operations
    Replies: 1
    Last Post: 06-07-2006, 07:56 PM
  4. GFI Breaker trips when I use the outlet
    By RENOPOOL in forum Pool Equipment & Operations
    Replies: 6
    Last Post: 05-23-2006, 08:49 PM
  5. pump trips ground fault breaker..
    By turnerd in forum Pool Equipment & Operations
    Replies: 2
    Last Post: 05-23-2006, 01:42 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts