    Default Central Boiler Hookup to Pool/Spa

    Has anyone ever tried to hookup a wood burning central boiler to head a pool/spa and pool in the fall and winter? Does anyone have any lessons learned or best practices? I have a 16,000 gal in ground pool and was wondering how it would work?

  2. #2
    Poconos is offline SuperMod Emeritus Whizbang Spinner Poconos 4 stars Poconos 4 stars Poconos 4 stars Poconos 4 stars Poconos 4 stars Poconos 4 stars
    Join Date
    Dec 1969
    Location
    Honesdale PA
    Posts
    1,812

    Default Re: Central Boiler Hookup to Pool/Spa

    As long as the BTU output of your heater meets your needs then I suppose it should work fine. 1 BTU raises 1 pound of water 1 F degree and it's about 7.5 pounds per gallon for water.
    Al

  3. #3
    Join Date
    May 2010
    Location
    Houston
    Posts
    32

    Default Re: Central Boiler Hookup to Pool/Spa

    I guess this would 16000 gals x 7.6lbs/gal x 30deg = 3,468,000 btu need if I was going to raise the temp 30 degs but I guess that would also need some time of time element in the calculation also. Let me go check my pump model and with gal/min I should be able to come up with a btu/hr I'd need. I may need to see just what the flow rate is to the house is also to see if there is any excess capacity.

  4. #4
    BigDave's Avatar
    BigDave is offline Lifetime Member Whizbang Spinner BigDave 3 stars BigDave 3 stars BigDave 3 stars
    Join Date
    Jul 2010
    Location
    New Jersey
    Posts
    1,932

    Default Re: Central Boiler Hookup to Pool/Spa

    Are you planning to put the pool water directly through the boiler or use some sort of heat exchanger to keep the boiler water and pool water separate?
    This may be a silly question but, does the boiler make steam? A condensing heat exchanger could be configured to use gravity to return the condensed steam to the boiler. Such a design wouldn't need a pump to move the boiler water.

    Your 3.5M btu would be delivered over time. You would also need to overcome the heat lost to evaporation, convection, conduction, etc. while trying to raise the temperature of the pool. Do you have a heater on the pool now? That could give you an empirical estimate of your losses.

    You'll need enough spare (btu/hr) capacity in the boiler to heat the water at the rate you desire and overcome the loss rate. The heat exchanger would have to have the same capacity.

    Sounds interesting from a tinkerer / wannabe engineer point of view.
    12'x24' oval 7.7K gal AG vinyl pool; ; Hayward S270T sand filter; Hayward EcoStar SP3400VSP pump; hrs; K-2006; PF:16

+ Reply to Thread

Similar Threads

  1. Central Texas New Guy
    By TXREALTOR in forum General Interest
    Replies: 2
    Last Post: 08-07-2012, 04:09 PM
  2. Central Valley SWCG w/ Low CL & High PH...
    By nomar116 in forum Salt Generators (SWCG) & other Chlorine Feeders
    Replies: 14
    Last Post: 12-16-2010, 09:04 PM
  3. Pump run-time in the Central-Texas winter?
    By aquarium in forum Pool Equipment & Operations
    Replies: 11
    Last Post: 02-08-2007, 01:56 PM
  4. Booster pump motor seizing with fountain hookup?
    By rtpatter in forum Pool Equipment & Operations
    Replies: 0
    Last Post: 08-06-2006, 08:11 PM
  5. Need help/advice complete pool renovation Central Florida
    By floridanative in forum In-Ground Pool Construction and Repair
    Replies: 0
    Last Post: 04-26-2006, 12:19 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts