The TropiCal will indicate on the instrument panel if there are any refridgerant problems so I don't think this is it. To determine why is has not increased, we can determine how much run time is needed to increase the temperature.
You have 12,000 gallons. What was the temperature that you started at? What temperature did you want to achieve? Is your pool covered with a solar blanket? What is the ambient air temperature? Which model TropiCal heat pump do you have (how many BTU's)? How many hours per day is the pump running?
12,000 gallons x 8.3 lbs/gallon = 99,600 lbs.
It takes 1 BTU 1 hour to heat up 1 lb of water 1 degree. Therefore it takes about an hour to heat up 99,600 lbs with a 100,000 BTU heat pump.
If the pump is turned off overnight, an uncovered pool will lose 50% of the heat added. That is, if you add 5 degrees during the day, an uncovered pool will lose 2.5 degrees overnight, which adds back to the amount of heat you have to put back in the following day. If you have been running the heat pump continually, you should have added 28 degrees, theoretically. Again, this will depend on the air temp, BTU rating of the heat pump, and pump run time.
Colder air temps reduce efficiency. Debris along the evaporator coil will reduce efficiency (make sure there are no leaves or debris blocking air flow to the evaporator coil). Too much water flow will reduce efficiency (25 - 70 gpm is recommended with 30 - 50 being more ideal).
Hope this helps.