Re: proper equipment?
Good to hear all is well again. As for the wiring, depends on the length of the run. I assume it's a 240 volt motor so that would pull about 7 amps as I measured mine. From copper wire tables the resistance of #14 gauge is 2.58 ohms oer 1000 feet, #12 gauge 1.62, #10 gauge 1.02 ohms per 1000 ft. If we assume a 100 foot run the total resistance in ohms works out to be .516 ohms for #14 gauge, .324 for #14 gauge, and .204 for #10. The resistance was for a single wire so you had to double it, 100' actually is 200' of conductor. At the 7 amp load the voltage loss is 3.612 volts for #14, 2.268 for #12 and 1.428 for #10. Any of these would have little effect on the motor or performance however from an efficiency standpoint you are losing about 25 watts of energy with the #14, 16 for #12, and 10 watts for #10. In general the less loss the better so I'd go with #10 which is still somewhat easy to handle and relatively reasonable cost. I have no idea what the electrical codes say or what local codes may dictate. Some electrical codes make no sense to me but Ohms Law always makes sense.
Hope this helps and of there are any questions please ask.
Al