I have several Jandy PHP pumps associated with my new pool installation (waterfall,etc) . these pumps are dual 115/230 Volts. Is there any major advantage to wiring at 230 versus 115 volt? I know less amps is less I^2R losses ,so 230 V operation may be a bit more efficient. Anything else? If not I will probably eat the incremental losses and wire at 120 Volts for compatibility with my X10 home automation system. Thanks in advance for any input.

Poconos
07-25-2006, 06:41 PM
Pump will run a little cooler at the higher voltage but the losses are the only difference I know of. If you're willing to accept that then go for convenience and simplicity.
Al

thepoolman1
07-25-2006, 09:22 PM
You might need larger or more breakers if you go with 120 volts. Larger wire also might be needed. X-10 makes several devices that will control 240 volt loads. Go with the 240, you'll be happier in the end.

CJDahl
07-25-2006, 10:07 PM
I have not been able to find any X10 switch or relay rated for 240 V load and outdoor use. Can you provide any specifics . thanks again for any assistance. Curt

Poolsean
07-25-2006, 10:21 PM
Radio shack has X10-230V modules, usually for appliances.
You'll not really save any money by running 230 volts (it costs the same: 230V @ 7 amps = 115 V @ 14 amps; P (power in watts) = I (current)x V(volts))
However, as thepoolman said, you'll save in breaker rating and wire gauges.

GHM
07-26-2006, 08:03 AM
Hi
My whole house is automated with a lot of X10 devices and controled with Homeseer software.
My experience is to stay away from most of the junk that x-10 makes.
Here is what I use to control my 220V pumps.
http://www.smarthomeusa.com/ShopByManufacturer/ACT/Item/RB104/
Works absolutely 100% reliable.
To make it weather poof I have it installed in a sealed pvc electrical box with my wiring in pvc conduit back to the panel.

CJDahl
07-26-2006, 07:39 PM
Thanks much !! This appears exactly what I was looking for.