View Full Version : Variable Speed Pumps
Extreme21
08-29-2013, 05:29 PM
I want to upgrade my Sta-Rite Max-E-Glas II pump to a more energy efficient variable speed pump. My pool is 19x23 13,500 gallon pool that is 5ft in the deepest section with no spa attached, and I want to make sure that I am not going to purchase a pump that is overkill for my size pool. I am averaging 28 kWh a day at an average cost of .22 and hour. I originally was going to purchase the Pentair Intelliflo VS, the saw that Hayward has the Max-Flo VS which is less horsepower and $$, and explains that it will save the same amount of money as the Pentair. Does anyone have any info that would help me decide. Attached are photos of my pool equipment setup.IMG_1167.jpgIMG_1173.jpgIMG_1170.jpg
mas985
08-30-2013, 11:19 AM
The Max-Flo VS is a lower head pump and it is actually more "efficient" (higher energy factor) than some of the bigger pumps. So it is a pretty good choice at a great price point. The only downside to it is that it would not work well for a pool with a spa where the VS would need to run the jets too. But everything else would work fine.
Here is a spreadsheet comparison I did some time ago for $0.20/kwh which is close to yours.
https://dxodqa.bn1.livefilestore.com/y2pUDmC36HTw1MikJezL_8CjSbdHk6aJCZdYuw1JG_Fbodq_XZ 4HfrjXIAqgWRW1bok5zpcG0lj3kIZchD8mltOJjxrFSX8x1lX6 51H4jEacBw/PumpEnergyCosts20.jpg?psid=1
PoolDoc
08-31-2013, 10:11 AM
Thanks for that very helpful response, Mark.
PoolDoc
08-31-2013, 10:12 AM
One question -- how did you determine motor efficiency?
mas985
08-31-2013, 10:55 AM
The efficiency comes from the CEC/APSP database but I am not using it in any of the calculations. It is information only. I believe it represents the full load motor efficiency so it really isn't relevant for a specific operating point. Also, it doesn't really have a correlation to which pump has the better operating cost either.
PoolDoc
08-31-2013, 12:32 PM
Do you know if whether V*A gives a close approximation to watts, or whether the power factor is large enough (or small enough) to make that inaccurate?
Extreme21
08-31-2013, 04:36 PM
Mark,
Thank you for the response. The chart is very helpful.
Matt
mas985
08-31-2013, 06:25 PM
Do you know if whether V*A gives a close approximation to watts, or whether the power factor is large enough (or small enough) to make that inaccurate?
V*A is certainly an upper limit because it assumes a PF of 1 but over a pump's head curve, the motor load can vary from around 40% to 100% and the power factor is dependent on load. At peak load the PF is usually not better than 0.9 but I haven't measured it directly on a pump. The following paper shows some of the effects but in general, I don't think you can count on the PF being close to 1 for an induction motor. There is always a reactive part to the power.
http://www1.eere.energy.gov/manufacturing/tech_assistance/pdfs/10097517.pdf
The best way to measure pump power is by using the power company meter on the side of the house. You can get a measurement with the pump vs off and get a much better estimate as long as nothing else changes in the house between measurements. I have a digital meter and it is pretty easy to get the power difference but you can do the same with the old style analog meters too.